At what duty cycle????

From: Robert Johnson [mailto:[email protected]] 
Sent: Monday, May 05, 2003 10:48 AM
To: 'JP Hare'; [email protected]
Subject: RE: AC outlet max current



A noncontinuous load is permitted to use 100% of the circuit rating. Only
continuous loads need the derating.

Bob Johnson
ITE Safety
 


From: [email protected]
[mailto:[email protected]] On Behalf Of JP Hare
Sent: Thursday, May 01, 2003 12:20 PM
To: Gonzalez, Kenneth P (Rocky); [email protected]
Subject: RE: AC outlet max current


Hi Rocky,

Article 210 of the NEC lists the requirements for branch circuits and
associated receptacles.  Table 210.21(B)(2) shows the receptacle load limits
and section 210.23 discusses the permissible loads in more detail.

On a related topic, I recently had a discussion with a colleague regarding
the plug for a certain North American hand-held hair dryer.  The ratings on
it are 1875 watts, 125 volts.  That puts it right at a 15 amps.  However the
plug is an ungrounded polarized NEMA 1-15 type with a built in GFIC.  This
allows it to be plugged into any standard 15 amp receptacle that you find in
the US.  Knowing the 80% requirement for cord-and-plug-connected loads, I
questioned how an NRTL could list this device.  It would seem that a 5-20
plug (perpendicular blades) would be necessary so that a 20 amp receptacle
would have to be used.

Our thoughts ranged from the cynical "money talks" theory to a more
logically based engineering justification.  (The code says that bathroom
receptacles must be on their own 20 amp branch with no other receptacles.)
But we never came to a final conclusion on why an NRTL would allow a 15 amp
plug-and-cord load to be plugged into a 15 amp receptacle.

Maybe our peers on the EMC-PSTC listserv have some ideas?

Regards,
J.P. Hare





This message is from the IEEE EMC Society Product Safety Technical Committee
emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line. All
emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to