Others have correctly identified the typical configuration. This can also be
generated by an open delta (two transformers). This is sometimes used to
provide three phase service to a small business customer with only one or
two three phase loads. You start with the customary 120/240 single phase
center tapped service, and with only one more transformer you add the third
leg with a 240 volt winding (you need the three primary phases to begin
with). It's a cheap solution with lower efficiency, but it works.

Bob Johnson
ITE Safety
 


From: [email protected]
[mailto:[email protected]] On Behalf Of Richard Meyette
Sent: Thursday, June 05, 2003 7:52 PM
To: [email protected]
Subject: 3-Phase Power Question


Here's a question for the power engineers in the group.

I measured the following phase voltages for the 3-phase power lines feeding 
a breaker box:

        phase to phase (all three phases) = 240V

        phase to neutral (2 of 3 phases) = 120V

        phase to neutral (1 of 3 phases) = 208V

Normally you would expect the phase to phase voltages to measure 208V and
the phase to neutral voltages to measure 120V for a Y-connected transformer.

What kind of power transformer configuration would provide these phase 
voltages?

Thanks in advance to anyone who can shed some light on this,

Richard Meyette
[email protected]






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to