In message <[email protected]>
   Richard Meyette writes:

> I measured the following phase voltages for the 3-phase power lines feeding 
> a breaker box:
> 
>       phase to phase (all three phases) = 240V
> 
>       phase to neutral (2 of 3 phases) = 120V
> 
>       phase to neutral (1 of 3 phases) = 208V
> 
> Normally you would expect the phase to phase voltages to measure 208V and
> the phase to neutral voltages to measure 120V for a Y-connected transformer.
> 
> What kind of power transformer configuration would provide these phase 
> voltages?

This is not a Y-connection, rather a delta connection with one center-
tapped phase.

This is a quite well known scheme in which a delta supply has a tap 
half way along one phase, so that single-phase loads can be supplied 
at half the line voltage, i.e. 120V for a 240V delta supply.

There is a good explanation at

http://www.franceformer.com/foreign_current/home.htm

This scheme is quite common in Caribbean countries, e.g. Bahamas and 
Jamaica.  Single-phase 120V appliances are connected between the 
outers of the center-tapped phase and center tap, 240V across the 
other two phases.  The 208V connection is normally not used.

Bill Lyons

-- 
Claude Lyons Limited 
Brook Road, Waltham Cross, Herts EN8 7LR, UK
Specialists in power and voltage control
Tel: +44 (0)1992 768888 
Fax: +44 (0)1992 788000
URL: http://www.claudelyons.co.uk





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to