Richard, I recognize that system.

It is a 3 phase delta with one of the sides tapped in the middle for the
neutral.  I haven't seen one since the late 50's, and then only in the
oldest sections of downtown Houston.  The scheme provided 3 phase service to
AC compressors and air handlers, and also supplied 110 volts for lighting
and office equipment.

The 208 phase you found was then known as the "wild phase" or the "stinger
leg". It was about 190 volts when the phase to phase voltage was 220.  The
relationship to 240 does work out; 190 X (240/220) = 207; nearly what you
found.

If you look outside the building you should be able to see the transformer
connections to confirm this.

I had almost forgotten such a thing ever existed.


Lou Aiken, LaMer LLC
27109 Palmetto Drive
Orange Beach, AL
36561 USA

tel ++ 1 251 981 6786
fax ++ 1 251 981 3054
Cell ++ 1 251 979 4648

From: Richard Meyette <[email protected]>
To: <[email protected]>
Sent: Thursday, June 05, 2003 6:51 PM
Subject: 3-Phase Power Question


>
> Here's a question for the power engineers in the group.
>
> I measured the following phase voltages for the 3-phase power lines
feeding
> a breaker box:
>
> phase to phase (all three phases) = 240V
>
> phase to neutral (2 of 3 phases) = 120V
>
> phase to neutral (1 of 3 phases) = 208V
>
> Normally you would expect the phase to phase voltages to measure 208V and
> the phase to neutral voltages to measure 120V for a Y-connected
transformer.
>
> What kind of power transformer configuration would provide these phase
> voltages?
>
> Thanks in advance to anyone who can shed some light on this,
>
> Richard Meyette
> [email protected]
>
>
> -------------------------------------------
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
>
> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>
> To cancel your subscription, send mail to:
>      [email protected]
> with the single line:
>      unsubscribe emc-pstc
>
> For help, send mail to the list administrators:
>      Ron Pickard:              [email protected]
>      Dave Heald:               [email protected]
>
> For policy questions, send mail to:
>      Richard Nute:           [email protected]
>      Jim Bacher:             [email protected]
>
> Archive is being moved, we will announce when it is back on-line.
> All emc-pstc postings are archived and searchable on the web at:
>     http://www.ieeecommunities.org/emc-pstc
>



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to