Hello all,
 
Just as an FYI, IEC 61010-1, third edition is at CDV status. I am hoping that
the members of TC 66 are taking note of these issues and will take them under
consideration so the standard is meaningful for those who use it. 
 
Best regards,
Ron Wellman


From: [email protected] 
mailto:[email protected]]On Behalf Of John Allen
Sent: Wednesday, December 01, 2004 1:40 AM
To: 'Camille Good'; - EMC PSTC Posts (E-mail)
Cc: Roger Mccoy
Subject: RE: IEC/EN 61010-1, 2001 'Circuits derived from Mains Circuits'



Camille 

In addition to the errors you mention, there are quite a large number of basic
typographical errors - especially with respect to various
figures/illustrations and the relevant cross-references in the text.

Take a careful look at the document and you will gradually see this. 

IMHO (as an Ex-BSI standards project manager, and a drafter/reviewer of many
in-company procedures and process documents), the range of definitions is
woefully incomplete and confusing, the  text is generally poorly drafted and
quite ambiguous in many places, and together these lead to problems where
there is no clear answer to some obvious questions with huge implications
(like the ones I posed!) nor clear indication of where suitable answers could
be found.

Regards 

John Allen 
ERA Technology Ltd 


-----Original Message----- 
From: Camille Good [ mailto:[email protected]] 
Sent: 30 November 2004 20:03 
To: - EMC PSTC Posts (E-mail) 
Cc: Roger Mccoy 
Subject: RE: IEC/EN 61010-1, 2001 'Circuits derived from Mains Circuits' 


I would definitely agree that 61010-1 is confusing! 
However, what are the errors in 6.7.3.2 and Table 9? 
I remember there was some discussion on this list a 
while back about errors in some example calculations, 
is that what you are referring to or is it something 
else?  If it is something else, was it discussed in 
this group (and therefore I should be able to find it 
in the list archives) or was it discussed somewhere 
else? 

Thanks in advance! 
-Camille 

--- Brian O'Connell <[email protected]> wrote: 

> Mr. Allen, 
> 
> My "personal rule" is either the apparatus is 
> ultimately connected to mains, 
> or it is not; and various NCBs has supported that 
> analysis. 
> 
> For an apparatus connected to mains, refer to Annex 
> D to determine 
> insulation requirements. Also, see 3.5.5, 3.5.6, and 
> 4.3.2.4. 
> 
> Section 6.9 also indicates insulation types, 
> according to the shock hazard. 
> 
> For apparatus not connected to mains, you can 
> determine the over-voltage 
> that it may be subject to, and may decide to use the 
> formula in 6.7.3.2 . 
> 
> As you know, 6.7.3.2 and Table 9 have errors. 
> 
> IMO, IEC 61010-1 as a test standard for end-use 
> apparatus, is more confusing 
> than most LVD standards. I suspect that many answers 
> can only be found in 
> the standards listed in Annex ZA. 
> 
> luck, 
> Brian 
> 
> -----Original Message----- 
> From: John Allen [ mailto:[email protected]] 
> Sent: Tuesday, November 30, 2004 5:27 AM 
> To: - EMC PSTC Posts (E-mail) 
> Subject: IEC/EN 61010-1, 2001 'Circuits derived from 
> Mains Circuits' 
> 
> Hi Folks 
> Sub-Clause 6.7.3.1 "Clearance values - General" and 
> Table 5 of Clause 6.7.3. 
> "Circuits other than MAINS CIRCUITS" refers to the 
> term 'Circuits derived 
> from MAINS CIRCUITS'. 
> However, nowhere in the standard are there clear 
> definitions or ranges of 
> examples of what these circuits are, or of what they 
> are not! Neither are 
> there any references to other standards to provide 
> this distinction. 
> Therefore one cannot point clearly to a methodology 
> for deciding what is, or 
> is not, a 'Circuit derived from Mains Circuits'  - 
> except possibly that a 
> totally battery powered unit with no charging 
> facilities probably is NOT a 
> 'Circuit derived from Mains Circuits' ! 
> This leads me to the following questions: 
> a) Where, if anywhere, is the dividing line between 
> the two? 
> b) If there is a dividing line, then how many layers 
> of definable compliant 
> insulation, isolation, barriering, transient 
> reduction measures, etc., do 
> you need to need between one and the other? 
> c) If there is not a dividing line, then how the 
> H*ll do you make the 
> distinction and so be able to apply the standard? 
> Thus, if anyone can shed some light on the unspoken 
> meanings of this part of 
> the standard, I would be most grateful! 
> Thanks in advance. 
> John Allen, 
> 

---------------------------------------------------------------- 
This message is from the IEEE Product Safety Engineering Society 
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators: 

     Ron Pickard:              [email protected] 
     Scott Douglas             [email protected] 

For policy questions, send mail to: 

     Richard Nute:           [email protected] 
     Jim Bacher:             [email protected] 

All emc-pstc postings are archived and searchable on the web at: 

    http://www.ieeecommunities.org/emc-pstc 

_____________________________________________________________________ 
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com



**********************************************************************
Copyright ERA Technology Ltd. 2004. (www.era.co.uk). All rights reserved. The
information supplied in this Commercial Communication should be treated in
confidence. 
No liability whatsoever is accepted for any loss or damage 
suffered as a result of accessing this message or any attachments.
**********************************************************************

_____________________________________________________________________
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com
---------------------------------------------------------------- This message
is from the IEEE Product Safety Engineering Society emc-pstc discussion list.
Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/listserv/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Ron Pickard: [email protected] Scott Douglas [email protected] 


For policy questions, send mail to: 


Richard Nute: [email protected] Jim Bacher: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc

---------------------------------------------------------------- This message
is from the IEEE Product Safety Engineering Society emc-pstc discussion list.
Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/listserv/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Ron Pickard: [email protected] Scott Douglas [email protected] 


For policy questions, send mail to: 


Richard Nute: [email protected] Jim Bacher: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 


Reply via email to