Tim,
 
C13 / C14 connectors (IEC60320 rated at 10A for John Woodgate's benefit) are
only rated at 10A, so fusing at 20A seems incorrect. You really need to
condsider the current rating of the equipment. Any power cord fitted with a
C13 connector will have either a 13A (for UK) or 16A (rest of EU) connector
and will be fused at 13A in the plug for the former case, or at 16A in the
power circuit in the latter. Either way, your coupler is only rated at 10A, so
why the 20A fuse?
If your equipment draws more than 16A, then the choice of coupler is incorrect
and you need to be looking at a C20 connector, which would probably connect to
a 32A power circuit via an IEC60309 connector or by permanent wiring.
If your equipment does only draw less than 10A, then I would recommend
replacing the fuse with one complying with IEC60127 standards rather than the
UL standard. It is possible that your equipment employs a switched mode power
supply, in which case it will consume half the current in the EU that it
consumes in North America on account of the supply voltage difference.
Best regards 

Neil R. Barker CEng MIEE FSEE MIEEE 
Manager 
Compliance Engineering 
e2v technologies (uk) ltd 
106 Waterhouse Lane 
Chelmsford 
Essex CM1 2QU 
UK 

Tel: (+44) 1245 453616 
Fax: (+44) 1245 453410 
Mob: (+44) 7801 723735 


From: [email protected] [mailto:[email protected]]
Sent: 17 February 2006 01:33
To: [email protected]
Subject: Safety question for ITE


Hello everyone,
 
I Need help to decide on FUSE value for ITE equipment. We are using power
suppy which has UL rated 20A fuse and C14 inlet, the question I have is it OK
to ship this product to Europe with power cords which use C13 connector?
 
Regards,
Tim Pierce

- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas [email protected] Mike Cantwell [email protected] 


For policy questions, send mail to: 


Jim Bacher: [email protected] David Heald: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 


Reply via email to