On 4/1/2008, Charles Blackham wrote:


Does anyone have any experience of providing useful lightning protection for
outdoor mounted equipment under these conditions? 



Hi Charles:

I have some experience with telecom installations where the ground connection
to the primary protector for a twisted copper pair is disconnected.  That
scenario occurs more often than many people realize.  However, due to way that
the wireline PSTN is constructed, there is a "reasonable" upper bound on
induced (not direct) lightning surges of about 5 KV.  So, if a manufacturer
wants their equipment to survive whether or not the primary protector is
functioning, the equipment can simply be designed to withstand 5 KV on the
wireline ports.

You don't provide many details on the equipment you are working with, so it is
hard to comment on your options for an ungrounded protection strategy.  The
main benefit of having a hard wired protective ground is to ensure that the
lightning return current takes a known, safe path to ground instead of an
unpredictable path that travels through sensitive circuitry.  If the equipment
does not contain a path to ground, it will not attract lightning return
currents in the first place.  So, if there is a way to make the equipment
fully isolated from ground up to the level of induced surges that you expect,
you can protect the equipment that way.




Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
[email protected]
http://www.randolph-telecom.com <http://www.randolph-telecom.com/> 


- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas [email protected] Mike Cantwell [email protected] 


For policy questions, send mail to: 


Jim Bacher: [email protected] David Heald: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 


Reply via email to