Hi Brian:

Wire ampacity ratings are based on the thermal characteristics
of the wire insulation.  The insulation will fail due to 
temperature long before the copper will melt.

Wire temperature ratings are marked on the surface of the 
wire insulation.  Temperature ratings range from 60 C to over
300 C.  

Wire temperature ratings are based on a single conductor in
free air.  As John Woodgate has pointed out, when wires are
bundled together into a cable, all of the wires contribute
to the temperature rise (and limit the thermal dissipation of
individual wires), so each individual wire must be derated 
accordingly.  In a cable, this derating can be very 
significant.  

Thermal degradation is a function of absolute temperature,
not temperature rise (as has been specified in some safety
standards).  

Thermal degradation is also a function of time at a high 
temperature.  

If a fault is likely to persist, then the insulation 
temperature rating should be based on the fault-condition
temperature.  If the fault current is not likely to persist
(for example, due to a fuse or circuit-breaker operation),
then the temperature rating may be based on the normal-
condition temperature.  Insulations do not fail 
instantaneously when the temperature exceeds the rated
temperature.  

Wire terminations and connectors have contact resistance,
which is almost always higher than the incremental resistance
of the wire.  Overheating is more likely at these points than
the wire itself.  (However, beware of coiled wire which acts
like a bundle and can easily overheat even though the current
is below rated ampacity of the wire.)


Best regards,
Richard Nute
Product Safety Consultant
Vancouver, Washington, USA



> -----Original Message-----
> From: [email protected] [mailto:[email protected]] On Behalf 
> Of Kunde, Brian
> Sent: Tuesday, August 02, 2011 5:36 AM
> To: [email protected]
> Subject: RE: Electrical design challenge
> 
> 
> Richard,
> 
> You bring up a point which I have debated many times in the 
> past. Since the wire can handle more current in a fault 
> condition than it is rated, the only real way of knowing is 
> to do an overload test as you suggested? Slowly increase the 
> output load while measuring the wire temperature until the 
> PSU shuts down or the wire overheats. Since this would 
> simulate a fault condition, do we use 150ºC (calculated for a 
> 40ºC ambient) as our upper limit for the wire temp? Is this 
> how it is done?
> 
> When we have done this test in the past we generally find out 
> the wire can handle much more current than we thought, but 
> connectors tend to overheat first, so don't forget to check 
> the connectors.
> 
> It is too bad that the world isn't designed so you can take a 
> 10A output, run it through a 10A wire, a 10A connector, and a 
> 10 amp load and not have to worry about what happens in a 
> fault condition.
> 
> The Other Brian
> 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to