Ok, brain damaged after several long nights as a code monkey -
did not finish my answer.

as you know, the last choice is delimited by
"Where an overcurrent protective device is used, it shall be a
fuse or a non-adjustable,
non-autoreset, electromechanical device."

Because electromechanical devices cannot meet the cycle
(reliability) requirments of IEC60730, they are not allowed. As
breakers age, there trip level and time-to trip may not always
age gracefully. Also, there is the risk that an operator may
attempt to hold the breaker closed during overload.

In any case, UL60730-1A states
DVD.4.1 A power limiting component - resistor, positive
temperature coefficient THERMISTOR, diode, or the like - employed
to limit the output of a power source to within the required
current or power levels, or otherwise relied upon to comply with
the performance requirements in Sub-clause DVD.6 shall have
permanence and stability so as not to decrease its limiting
capabilities. Among the factors considered when determining the
acceptability of a power limiting component are:
a) Effect of operating temperature,
b) Electrical stress level,
c) Effect of transient surges,
d) Resistance to moisture,
e) Endurance,
f) Temperature change shock, and
g) If appropriate, thermal runaway.


R/S,
Brian 


From: Brian O'Connell [mailto:[email protected]]
Sent: Tuesday, June 17, 2008 6:50 AM
To: 'Jim Eichner'; '[email protected]'
Subject: RE: 60950-1:2006 clause 2.5 - Limited power sources


Logic error - the requirements of cl 2.5 are connected by 'OR'
logic. Note that one of the choices is
"b) a linear or non-linear impedance limits the output in
compliance with Table 2B. If a
positive temperature coefficient device is used, it shall pass
the tests specified in IEC60730-1, Clauses 15, 17, J.15 and J.17;
or"

Assuming that this is for a mains-isolated LPS output, we can say
that this is not related to overcurrent protection for branch
circuits, and will also assume that another overcurrent
protective device is being used to satisfy NEC 240.10.

If the above is true, then a PTC, that is certified as a current
interrupt where the end-use meets its conditions of
acceptability, should be acceptable if a short or overload meets
the limits of table 2C.

I have used 'auto-resetting' PTCs to meet the requirements of
both UL60950-1 and UL1012, their use IS, in fact, allowed. But I
have also 'encouraged' the designers to include other series
impedances that will also provide ultimate current limits not
dependent on the PTC.

luck,
Brian 


From: [email protected] [mailto:[email protected]]On Behalf Of
Jim
Eichner
Sent: Tuesday, June 17, 2008 2:24 AM
To: [email protected]
Cc: Jim Eichner
Subject: 60950-1:2006 clause 2.5 - Limited power sources

If an overcurrent protective device is used, it is not allowed to
be
auto-resetting.  Why?  Just above this requirement is an
allowance to
use PTC's and they auto-reset, so why the bias against auto-reset
breakers?

Thanks,

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: [email protected]
web: www.xantrex.com 

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]