The breaker, in this case is not used to interrupt current from a
branch ckt, but to meet the requirements for LPS limits of a
secondary ckt.

Also in this thread, Mr. Nute had stated that safety standards
may not be addressing reliability. The problem here might be
specific to North American (NEC/CEC) requirements, where the
applicable safety standard for an LPS would probably be UL1012,
CSA107, and/or CSA220. In addition to the OP, I would also like
to know if this is the source for not allowing breakers to meet
LPS limits.

An LPS, in addition to the requirement to be safe for human
contact, must also not be a fire hazard when used in cable trays
and industrial wiring conduits that are used for non-mains
signals and control voltages. The NEC and CEC specify, somewhat
indirectly, what is considered a safe current interrupt device
for these conditions.

As for 'reliability', can we assume that safety standards such as
60730, 61058, 61015, 60384, etc address the issue of reliability
through a min number of cycles, or am I making an invalid
comparison of apples to oranges ?

Back to the lab to see if anything has melted...

luck,
Brian


From: [email protected] [mailto:[email protected]]On Behalf Of
John
Woodgate
Sent: Thursday, June 19, 2008 9:42 AM
To: [email protected]
Subject: Re: 60950-1:2006 clause 2.5 - Limited power sources

In message <002e01c8d226$d56ba150$c600a8c0@PC323541548743>, dated
Thu,
19 Jun 2008, 'Rich Nute' <[email protected]> writes:


>Circuit-breakers probably are not operated even 100 cycles
during their
>lifetime.

In order to meet the 60950-1 requirement to disconnect both mains
poles
because either may be live, a breaker is used as the main power
switch,
thus saving two fuses. Those breakers are used quite often.
--
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and
www.isce.org.uk
Either we are causing global warming, in which case we may be
able to stop it,
or natural variation is causing it, and we probably can't stop
it. You choose!
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc



Reply via email to