I do not know what "makes sense". LPS requirements are also
defined in several UL safety standards that are based on NEC, for
example, UL1012 ('Limited voltage limited energy') and UL508
('Limited voltage limited current'). In general, the NEC severely
limits allowable materials, external and connected to the power
source, that exceed specific, voltage, current, and/or VA levels.

IEC60364 also limits materials that may be used with a power
source that exceed certain voltage, current, and/or VA levels.

The ability to "pass safety" is dependent on the requirements of
the end-use equipment.

<Jerk Mode>
As all of these limits are clearly and specifically delineated in
safety standards, one could assume that the OP has not read the
standard, or will not purchase the standard.
</Jerk Mode>

<Free Advice Mode>
It worries me that some regulatory people seem do safety
engineering the same way that some design people do software
engineering - ad hoc and non-reproducible. For each new model
series, whether a component power supply or end-use equipment, I
do the following for the design engineer at start of project:
1. using applicable safety stds, I build a list of tables,
limits, and construction requirements and link each requirement
to a clause.
2. using applicable emc stds, I tabulate a list of emission
limits and immunity test levels, and link to the clause in the
product family std.
3. I grab a revision 'X1' schematic, do some basic calculations,
and red-line the schematic and PCB layout as soon as available.
4. Even if I do not submit test data to an agency or test house,
I NEVER send a sample to the safety or EMC labs without
performing in-house tests that indicate conformity to all checked
clauses that I checked in the applicable CBTR form - so I always
know that there is a good margin.
5. When a test house or safety agency rejects my data, or
indicates a failed sample, I NEVER accept their requirements or
test data at face value.
6. I never accept a passing agency report at face value. I verify
that all agency test data will support all applicable clauses in
the safety std.
7. When I do HALT at end of design cycle - I consider a test
condition that results in the unit not meeting a rating or
spacing requirement to be a fail level - it is NOT an operational
limit.
</Free Advice Mode>


From: [email protected] [mailto:[email protected]]On Behalf Of
Christine Rodham
Sent: Wednesday, January 21, 2009 12:38 PM
To: [email protected]
Subject: Re: Safety Experts: Limited Voltage Pwr Supplies vs.
Non-Limited Voltage Power Supplies

List Members,

Thanks for all the great replies!

Would it make sense to see if the end product can pass safety
with the non-LPS power supply?

Is the the LPS clause just a CB scheme requirement or is it
required for NRTL approval also?

Best regards,

Christine Rodham

Christine Rodham <[email protected]> wrote:
Hi List Members,

We have a vendor that provides us a unit that uses an external
power supply ( 90- 240VAC)
The power supply is labeled LPS after the model number which
means: Limited Voltage Power Supply.

They recently changed vendors to another power supply with the
EXACT same rating Except it was not marked as a LIMITED voltage
power supply.

Our supplier says this is not a compliance / safety issue because
both supplies are recognized by UL and have the same voltage and
current rating.

So the $64,0000 dollar question is can you use a non- LPS in
place of a LPS if they have the same rating?

Thanks in advance,

Thank you in advance!

Christine Rodham

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>


Reply via email to