You would also have to consider the frequency involved. At "very high"
frequencies you probably could not get a good RF ground no matter what
method you used to ground a hinged panel.

Bob Heller
3M EMC Laboratory, 76-1-01
St. Paul, MN 55107-1208
Tel:  651- 778-6336
Fax:  651-778-6252
===================================================================


                                                                              
                                      
  From:       John Cochran <[email protected]>                           
                                      
                                                                              
                                      
  To:         Doug Nix <[email protected]>                                         
                                      
                                                                              
                                      
  Cc:         "[email protected]" <[email protected]>       
                                      
                                                                              
                                      
  Date:       12/22/2009 11:39 AM                                             
                                      
                                                                              
                                      
  Subject:    RE: [PSES] Electrical components on hinged panels               
                                      
                                                                              
                                      
  Sent by:    <[email protected]>                                             
                                      
                                                                              
                                      





Thank you, Doug.  Looks like we have some rewiring to do.  I greatly
appreciate your finding this information for me.

Thanks,
John

From: Doug Nix [mailto:[email protected]]
Sent: Tuesday, December 22, 2009 11:12 AM
To: John Cochran
Cc: [email protected]
Subject: Re: [PSES] Electrical components on hinged panels

John,

Here is the relevant text. Bolding added for emphasis:
      EN 60204-1:2006

     11 Controlgear: location, mounting, and enclosures

     11.1 General requirements
     All controlgear shall be located and mounted so as to facilitate:
     - its accessibility and maintenance;
     - its protection against the external influences or conditions under
     which it is intended to
       operate;
     - operation and maintenance of the machine and its associated
     equipment.

     11.2 Location and mounting

     11.2.1 Accessibility and maintenance


     All  items  of  control gear shall be placed and oriented so that they
     can  be  identified  without moving them or the wiring. For items that
     require  checking  for  correct  operation  or that are liable to need
     replacement,  those  actions  should  be  possible without dismantling
     other  equipment  or  parts  of  the  machine (except opening doors or
     removing  covers,  barriers  or  obstacles).  Terminals  not  part  of
     controlgear   components  or  devices  shall  also  conform  to  these
     requirements.
     All controlgear shall be mounted so as to facilitate its operation and
     maintenance from the front. Where a special tool is necessary to
     adjust, maintain, or remove a device, such a tool shall be supplied.
     Where access is required for regular maintenance or adjustment, the
     relevant devices shall be located between 0,4 m and 2,0 m above the
     servicing level. It is recommended that terminals be at least 0,2 m
     above the servicing level and be so placed that copductors and cables
     can be easily connected to them.

     No devices except devices for operating, indicating, measuring, and
     cooling shall be mounted on doors or on normally removable access
     covers of enclosures. Where control devices are connected through
     plug-in arrangements, their association shall be made clear by type
     (shape), marking or reference designation, singly or in combination
     (see 13.4.5).

     Plug-in devices that are handled during normal operation shall be
     provided with non-interchangeable features where the lack of such a
     facility can result in malfunctioning.

     PIug/socket combinations that· are handled during normal operation
     shall be located and mounted so as to provide unobstructed access.

     Test points for connection of test equipment, where provided, shall
     be:
     - mounted so as to provide unobstructed access;
     - clearly identified to correspond with the documentation (see 17.3);
     - adequately insulated;
     - sufficiently spaced.

Normally this is taken to mean that pushbuttons, selector switches, pilot
lights, HMIs, cooling fans, and instruments may be mounted on doors or
removable covers. PLC's and remote I/O blocks are not normally included,
although you might be able to successfully argue that installing a remote
I/O block on the door lessens the amount of wiring that must cross the
hinge, and is therefore preferable to running discrete wiring.

Also note that there is a requirement for the wiring to be highly flexible:

     13.3 Wiring inside enclosures
     Conductors inside enclosures shall be supported where necessary to
     keep them in place. Non-metallic ducts shall be permitted only when
     they are made with a flame-retardant insulating material (see the IEC
     60332 series).

     It is recommended that electrical equipment mounted inside enclosures
     be designed and constructed in such a way as to permit modification of
     the wiring from the front of the enclosure (see also 11.2.1). Where
     that is not practicable and control devices are connected from the
     rear of the enclosure, access doors or swingout panels shall be
     provided.
     Connections to devices mounted on doors or to other movable parts
     shall be made using flexible conductors in accordance with 12.2 and
     12.6 to allow for the frequent movement of the part. The conductors
     shall be anchored to the fixed part and to the movable part
     independently of the electrical connection (see also 8.2.3 and
     11.2.1).
     Conductors and cables that do not run in ducts shall be adequately
     supported.
     Terminal blocks or plug/socket combinations shall be used for control
     wIFIng that extends beyond the enclosure. For plug/socket
     combinations, see also 13.4.5 and 13.4.6.
     Power cables and cables of measuring circuits may be directly
     connected to the terminals of the devices for which the connections
     were intended.

Section 12.2 deals with wiring materials, gauge and ampacity. Section 12.6
deals with the specific requirements for flexible cables. I'll leave you to
review those sections on your own.

Feel free to contact me with any questions.

Happy Holidays to all!
--
Doug Nix, A.Sc.T.
IEEE PSES Toronto Chapter
Toronto Section, Ontario, Canada

[email protected]
office: +1 (519) 650-4753
mobile +1 (519) 729-5704
fax +1 (519) 653-1318

Find me LinkedIn at http://www.linkedin.com/in/dougnix


On 22-Dec-09, at 09:27 , John Cochran wrote:


I have asked for the specific standard and clause that the inspector is
using to declare our cart is unacceptable for installing components on the
door.  The product is a mobile control station for use in industrial
process control.  It contains a server and UPS in the main enclosure, with
a Control Logix controller, Ethernet router and 24VDC power supply on the
door.  Main incoming power is terminated in the main enclosure through a
16A breaker and protective earth ground is permanently connected to the
stainless steel enclosure.  The power is then run to the UPS in the main
enclosure bottom, then out of the UPS to the door for distribution to all
the components through 5A breakers.  This also includes coming back across
the door hinge to the server and display.  A separate permanently attached
ground braid is run between the main enclosure and the door, to connect
protective earth to the door.  Guess I have to look at the EN60204 and see
if I can find any problems with our wiring practices.

John

From: [email protected] [mailto:[email protected]] On Behalf Of John Allen
Sent: Monday, December 21, 2009 9:10 PM
To: Doug Nix
Cc: [email protected]
Subject: Re: [PSES] Electrical components on hinged panels

Pretty sure it's allowed but would have to verify.  EN60204 should be the
Standard for the panel.  Ask the inspector to point to a Standard and
clause.



On Dec 21, 2009, at 5:50 PM, Doug Nix <[email protected]> wrote:
      John,

      Is this industrial equipment?

      --
      Doug Nix, A.Sc.T.
      IEEE PSES Toronto Chapter
      Toronto Section, Ontario, Canada

      [email protected]
      mobile (519) 729-5704
      fax (519) 653-1318

      Find me LinkedIn at http://www.linkedin.com/in/dougnix

      Fostering Technological Innovation and Excellence for the Benefit of
      Humanity. Celebrating 125 Years of Engineering the Future.
      http://www.ieee125.org

      On 21-Dec-09, at 17:51 , John Cochran wrote:



      Do you know if there is a CE compliance issue with attaching
      electrical components to a hinged door?  For ease of construction, we
      often attach components to the access door of our industrial control
      panel enclosures.  UL has evaluated our construction methods and
      certified us a UL508 Panel Shop.  Criteria is that a solid earth
      ground is attached to the door, and all electrical cables are
      protected against damage.  We are being told by a customer that
      electrical components are never allowed on a door, in compliance with
      CE.  If UL finds it acceptable, I am not sure why it would be
      unacceptable for Europe.  I have seen many enclosures in Europe with
      electrical components on a removable panel or door.  Is the inspector
      exercising personal preference, or is there a compliance standard
      that backs up this decision to reject our wiring practices?

      Thanks,
      John Cochran
      -
      ----------------------------------------------------------------
      This message is from the IEEE Product Safety Engineering Society
      emc-pstc discussion list. To post a message to the list, send your
      e-mail to <[email protected]>

      All emc-pstc postings are archived and searchable on the web at
      http://www.ieeecommunities.org/emc-pstc
      Graphics (in well-used formats), large files, etc. can be posted to
      that URL.


      Website: http://www.ieee-pses.org/
      Instructions: http://listserv.ieee.org/request/user-guide.html
      List rules: http://www.ieee-pses.org/listrules.html


      For help, send mail to the list administrators:
      Scott Douglas <[email protected]>
      Mike Cantwell <[email protected]>


      For policy questions, send mail to:
      Jim Bacher <[email protected]>
      David Heald <[email protected]>

      -
      ----------------------------------------------------------------
      This message is from the IEEE Product Safety Engineering Society
      emc-pstc discussion list. To post a message to the list, send your
      e-mail to <[email protected]>

      All emc-pstc postings are archived and searchable on the web at
      http://www.ieeecommunities.org/emc-pstc
      Graphics (in well-used formats), large files, etc. can be posted to
      that URL.


      Website: http://www.ieee-pses.org/
      Instructions: http://listserv.ieee.org/request/user-guide.html
      List rules: http://www.ieee-pses.org/listrules.html


      For help, send mail to the list administrators:
      Scott Douglas <[email protected]>
      Mike Cantwell <[email protected]>


      For policy questions, send mail to:
      Jim Bacher <[email protected]>
      David Heald <[email protected]>
-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to <
[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.


Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html


For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>


For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]>



-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to <
[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.


Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html


For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>


For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]>

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to