What is the rationale behind a vertical conducting surface for conducted
emissions?
 
Ken Javor

Phone: (256) 650-5261



________________________________

From: Wan Juang Foo <[email protected]>
List-Post: [email protected]
List-Post: [email protected]
List-Post: [email protected]
Date: Wed, 23 Sep 2009 13:46:27 +0800
To: <[email protected]>, <[email protected]>
Cc: Wan Juang Foo <[email protected]>
Subject: Re: Conducted emission measurements

Hello Tim,
I may be  missing.  Is there such a 40 cm height?  Here is my 5 ยข worth.  

These are some of the the special provision for conducted emission testing: 


        To meet EN 55011, I suppose since 1999?? the measurement may be carried 
out: 
        

                - on the radiated emission test site (same EUT configuration)
                - above a metal ground plane which shall extend at least
                 50 cm beyond the boundary of the equipment under test
                 and have a minimum size of 2m x 2m 
                - within a screened room; either the floor or one wall of
                 the screened room shall act as the vertical ground plane
                

        ..  CISPR 22 since (1993) and Amendment 1 (1995) 
        

                Table- top EUTis to be placed 40 cm from a vertical metal 
reference plane
(e.g. a wall of a screened room/enclosure)
                 "The EUT, where intended for table-top use, shall be placed 
0,4 m from a
vertical metal reference plane of at least 2 m by 2 m and shall be kept at
least 0,8 m from any other metal surface or other ground-plane not being part
of the EUT. If the measurement. is made in a screened enclosure, the distance
of 0,4 m may be referred to one of the walls of the enclosure."
                Floor- standing EUT on a horizontal metal ground- plane, not in 
metallic
contact with the ground- plane.   Metal floor of a screened room may replace
the reference ground- plane
                


best regards,
Tim Foo

Expert Witness, EMC and Product Safety 
ECE, School of Engineering,
http://www.np.edu.sg/ece/                          DID: +65 6460 6143
Ngee Ann Polytechnic, 
535 Clementi Road,                             Fax: +65 6467 1730
Singapore 599489

[email protected] wrote on 23/09/2009 06:06:05 AM:

> Hello Group,
>  
> I have a question about the conducted emission measurements 
> performed in a semi-anechoic chamber.
>  
> CISPR 22 requires the use of a vertical ground plane when testing 
> tabletop EUTs, unless you mount your EUT on a non-conductive table 
> 40cm above the horizontal ground plane (instead of the traditional 80cm)
>  
> I did not find a requirement for a vertical ground plane when 
> testing floorstanding equipment. If one opts to use the alternative 
> method of not using the vertical ground plane, can floorstanding 
> equipment also be tested without the vertical ground plane? The 
> horizontal ground plane is always present since that is the chamber floor.
>  
> What are most labs using? We have the option of making a removable 
> vertical ground plane "wall" or mounting the equipment on a 40cm table.
>  
> Thanks,
> Tim Pierce
> - 

________________________________

NOTICE:
This message may contain privileged/confidential information. If you are not
the intended recipient of this email, please delete it immediately and notify
the sender . 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to