Yes, and in the real world that is what is done. But it has to meet the accuracy requirement of the test. For example, see MIL-STD461E 4.3.1 (slightly snipped):

4.3.1  Measurement tolerances.
Unless otherwise stated for a particular measurement, the tolerance shall be as follows:
c. Amplitude, measurement receiver: ±2 dB
d. Amplitude, measurement system (includes measurement receivers, transducers, cables, and so forth): ±3 dB

If the receiver is already ±2 dB we don't have much to work with. Calibration with X4 TUR might require an accuracy of 0.25 dB. Might settle for less, no?

Sooner or later, someone will say their project passes by  0.5 dB;  SHIP IT.

Same old story.

Cortland
KA5S

On 12/7/2011 6:50 AM, Ken Javor wrote:
Now we get to the heart of the matter that prompted the original post.

That spike in the 137 cm tip-to-tip biconical used with a T1 dipole balun (28 -- 200 MHz) behavior might have been objectionable, but you wouldn't miss it an analog sweep with even 1% frequency steps. You would only miss it if you calibrated every ten MHz as was done with the biconical antenna design in MIL-STD-461A (1968 -- when swept performance was difficult to do). There is no need to use frequency steps commensurate with the sorts of BWs used during EMI testing. A 1 - 5 MHz BW would more than suffice to sweep an antenna used above 30 MHz to ensure not missing anything.

The following quote is the rationale I have seen a few places with which I take issue:

"Though the >sweep< may be continuous, if you can read amplitude only by marking pixels, you need to insure .5 BW or less per pixel. That's straight sampling theory, right?"

That is straight sampling theory applied to an unknown signal characteristic. If a continuous sweep using 1/2 BW steps as per sampling theory has been performed, then discrete points for an antenna factor file may be chosen by inspection so that in any particular frequency range either of the two following conditions are met:

 1. If the data is noisy, with no obvious trend, then frequency points
    should be listed so that the antenna factor between any two listed
    points doesn't change by more than 1 dB (or whatever delta is
    deemed necessary for adequate accuracy).
 2. If a linear or log-linear approximation can be made over some
    frequency interval, then only the two endpoints of that interval
    need be recorded, with the understanding that between those two
    points the appropriate interpolation will yield the desired
    accuracy. The interpolation has to be one which the automated
    software can be instructed to perform on its recorded antenna
    factor files.


One of these two approaches should work when deriving a set of discrete points from a continuous sweep of any test transducer factor's performance. The question is whether this is "cast in stone" anywhere or left up to the person doing the calibration, or the test engineer abstracting a subset of data points for inclusion in his files.


Ken Javor

Phone: (256) 650-5261


------------------------------------------------------------------------
**



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to