Maybe not. Most isos > 1kVA have a removable plate on end-bell housing where
the gnd terminal is exposed and can be disconnected. But body of xfmr must
always be connected to PE. If output floated and neutral not referenced to
PE, probably should have both output terminals fused.

Brian

-----Original Message-----
From: [email protected] [mailto:[email protected]]On Behalf Of Joe Randolph
Sent: Tuesday, February 14, 2012 11:43 AM
To: Grace Lin
Cc: [email protected]
Subject: Re: Isolation Transformers

On 2/14/2012, Grace Lin wrote:

We are preparing a product, with a transmitter module installed, to an Asian
country for in-country testing. We are instructed to have the module
installed in the end product during EN 300 328 transmitter testing
(conducted method). The product is powered by 230V AC. Our engineers tell me
if I do not isolate the ground, I will damage the receiver.

Hi Grace:

In selecting your isolation transformer, one thing to watch out for is that
many "isolation transformers" actually carry the ground path all the way
through.

I learned this several years ago when I bought a pair of Tripp-Lite
isolation transformers for use in my lab.  I had to re-wire them to obtain
the galvanic isolation that I was seeking.

My impression is that many of the "isolation" transformers that are
available on the market are intended for *noise* isolation, not *safety*
isolation.  The distinction is not always clear in the product literature.

Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
[email protected]
http://www.randolph-telecom.com

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to