Ed-

I have seen stuff like this. My company makes protective relays that 
control the power system. That means that these relays work with signals 
at 60 Hz (or 50 Hz for many parts of the world outside of North America). 
The test standards call for the use of 1 kHz amplitude modulation. The 
relays have analog and digital filters that will generally reject 
frequencies this high. So there can be circuits with marginal RF immunity 
that will pass the standard test. My fix for this is to also test using 60 
Hz amplitude modulation. If there are circuits that respond to RF, the 
resulting 60 Hz signal cannot be rejected by the filters, as this matches 
the frequency of the desired signal. I have detected many more marginal 
circuits using this method.

I view it as a deficiency of the relay-specific test standards that 60 Hz 
(or 50 Hz) AM is not specified for the test.

Donald Borowski
EMC Compliance Engineer
Schweitzer Engineering Labs
Pullman, Washington, USA



From:   "Ed Price" <edpr...@cox.net>
To:     <EMC-PSTC@LISTSERV.IEEE.ORG>
Date:   08/20/2012 08:03 PM
Subject:        RE: [PSES] 61000-4-3: Rate of application of field
Sent by:        emc-p...@ieee.org



Ken:
 
The biggest difference I see was that I called it ?rare? and you said it 
was ?very unlikely,? so that?s not much of a fight. J
 
To dip back into one very interesting program, I was running the qual 
testing on some soldier-worn electronics. We were doing the typical RS103 
exposure of 50 V/M using 1 kHz 50% duty cycle modulation. We had some 
marginal improper responses (stuttering of the expected response & false 
positive responses) at a few harmonically related frequencies in the low 
HF region. So, we go into the usual try-everything-we-can-think-of mode, 
the sorry-but-ferrite-beads-won?t-help 1 MHz mode, and then the 
let?s-try-anything mode. I?m sitting there watching the false responses 
mess up the error rate, and I inadvertently move the modulation frequency 
just a bit downward. Wow, the system crashed like a rock! It turns out 
that the system had some broadly resonant responses (hence the 
harmonically related HF points) that let energy in, but the real killer 
was the modulation rate. The system really hated (IIRC) something around 
960 Hz modulation (pulse or AM didn?t matter), although it would tolerate 
strong CW at any frequency. The system gurus later explained this as my 
modulation rate syncing with a harmonic of their data sampling rate; if I 
was just a bit off, then their error correction algorithm could cover the 
loss of data. However, if I was right on them, then every time they 
sampled, I had an RF jolt right in their front end.
 
The lesson was that 461 suggested we use 1 kHz as a default, but if we had 
studied the system with more diligence, we might have seen that some other 
modulation (960 Hz) would have been more a much more harsh condition. And 
of course, 461 testing is all about finding that worst-case scenario, not 
just proving that your gadget works most of the time. Thus, I often used 
modulations beyond the popular 1 kHz, 100 Hz, 1 Hz, 1 uS, 50% pulses  and 
AM stuff. (Which is all probably pretty boring to the commercial and EN 
guys on this list, so sorry.)
 
Ed Price
El Cajon, CA
USA
 
 
From: Ken Javor [mailto:ken.ja...@emccompliance.com] 
Sent: Monday, August 20, 2012 7:26 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] 61000-4-3: Rate of application of field
 
Going to pick a small nit with Ed. 

In our world, military and aerospace EMC, Ed is correct that some devices 
can respond more to a cw signal than to an amplitude demodulated signal. 
That is because the way we do AM, the rms power is higher for cw than for 
AM. This is because we define the test level as the rms equivalent of the 
peak of the modulation waveform.  Since 1993 MIL-STD-461 requires square 
wave pulse modulation. Clearly, there will be half as much power in that 
modulation than cw. But across the Pond, they add the amplitude modulation 
on top of the cw level, and add 5.1 dB more signal doing so. So it is 
highly unlikely that something would respond to an EN 61000-4-3 
unmodulated signal if it wasn?t already susceptible to the modulated 
waveform. 
 
Ken Javor
Phone: (256) 650-5261


From: Ed Price <edpr...@cox.net>
Organization: ESP Labs
Reply-To: <edpr...@cox.net>
Date: Mon, 20 Aug 2012 17:03:45 -0700
To: <emc-p...@ieee.org>
Subject: RE: [PSES] 61000-4-3: Rate of application of field

Brian:

??Other labs level the forward power at each frequency with modulation 
off, then turns on the modulation only for the dwell time, then turns off 
modulation ?? This technique increases the test time, but more 
importantly, it includes a double exposure, first to the CW RF field while 
the leveling is taking place, and then for the dwell time with the 
modulation turned on. I have seen EUT?s which were more sensitive to a CW 
field than to the modulated field. Granted, that was rare, but it can 
happen. You would need to consider the possibility that you may be 
?over-testing? using this technique. 
 
?This method would be more accurate and gives you a better verification 
method?? I wouldn?t say that. You may have any number of non-linearity?s 
in your RF signal path. Logically, you might say that if you were using a 
pulse modulation, then leveling on CW would accurately establish the 
level, and then all you would be doing is turning it off and on at the 
pulse rate. But in the real world, maybe your power amplifier changes 
output power with average loading. Oops, you could be applying a higher 
peak level during the modulated portion of your exposure. Essentially, 
leveling on CW and then applying modulation is sorting counting on a blind 
assumption that modulation doesn?t change the signal amplitude.
 
Applying the modulation, leveling the field and then sweeping (or 
stepping) is an older technique, but equally accurate. It makes the 
assumption that you know what the modulation envelope does to the detector 
that you use to monitor the field. For instance, if you wanted to apply a 
50% duty cycle pulsed RF field of 100 V/M peak, then the detector might 
read 100 V/M with a CW field, but would drop to the RMS value of a 50% 
duty cycle (70.7%, or 70.7 V/M) when the modulation was turned on. Of 
course, using RMS detectors with this technique has an inherent limit; 
when the duty cycle becomes much shorter than say 10%, it becomes very 
difficult to remain accurate.
 
As I see it, both techniques have shortcomings. The ?tune / level in CW / 
apply modulation / dwell / turn off modulation & RF / tune again? method 
leaves you wondering about what happens during the modulation time, and 
the ?apply RF / apply modulation / sweep (step)? method requires you 
understand the modulation effect on your measurements. I preferred the 
first method for low duty cycle and complex pulse modulations, but 
preferred the latter more direct method for CW or 80% AM modulated sine 
wave modulation.
 
All this discussion would be moot if we had true peak reading broadband 
field strength sensors, and if the immunity standards were all referenced 
in terms of peak applied field strength. Until then, we have to wrestle 
with techniques that are not perfect. Now why am I thinking of Lucha 
Libre?


Ed Price
El Cajon, CA
USA



From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
Sent: Monday, August 20, 2012 7:14 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] 61000-4-3: Rate of application of field


James,
 
What version of the standard are you looking at? The ?family? standard we 
use calls out the 2002 version but the latest version we have on-hand is 
the 2006 version.
 
I have noticed that different labs perform the test differently regarding 
how the power is established, verified, and how the modulation is applied. 
I do not see where the standard calls out the details of how this is 
performed during the test. I assume most labs are using whatever method 
they use which gives the most accurate results within the limitations of 
the test equipment and software they are using. 
 
For instance, some labs just set the signal generator output level that 
was established by the calibration and leave the modulation always turned 
on throughout the test. Other labs level the forward power at each 
frequency with modulation off, then turns on the modulation only for the 
dwell time, then turns off modulation and level at the next frequency. 
This method would be more accurate and gives you a better verification 
method, but as far as I can see this is not specifically called out in the 
standard. 
 
As far as gradually applying the carrier or modulation strength I really 
don?t know. The standard does not reference it as far as I can see.
 
One issue your email points out is the fact that EMC labs are performing 
the test differently which may or may not cause a larger variation in the 
results when comparing one lab to another. Our customers often ask about 
our test method and request variations to be made for one reason or 
another; often to try and match a test method from another lab that they 
use. 
 
The Other Brian
 

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Pawson, 
James
Sent: Monday, August 20, 2012 5:54 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: 61000-4-3: Rate of application of field


 

Hello,



I can't find any clauses in 61000-4-3 (radiated RF immunity) that deal 
with the rate of application of the RF field.



My understanding is that the test is generally performed by setting the 
unmodulated carrier to the level contained within the calibration file and 
then suddenly applying the modulation.



Is there any precedent for, or problem with, gradually increasing the 
modulated carrier field strength up to the required level instead of a 
more sudden application?



I imagine a system like a mobile radio would involve a suddenly applied 
burst of RF when the transmitter is "keyed".



Many thanks

James

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html