All,

Thank you for all this input to the wire nut question recast.  

Although it seems  these devices have gained some acceptance, I don't see any 
outright endorsements.  

I have used these myself and I am very aware of their shortcomings.  There are 
reasons wire splicing is not allowed in blind areas behind walls.  

I will not be recommending these any time soon for internal appliance wiring.  
In my mind these are still questionable in field wiring boxes if for more than 
a couple amps.  And I really dislike the 100% non-metallic types.  


Doug

Douglas E Powell
Independent Compliance Consultant
http://www.linkedin.com/in/dougp01
 
http://www.linkedin.com/in/dougp01

-----Original Message-----
From: Richard Nute <[email protected]>
Date:         Tue, 9 Oct 2012 16:45:01 
To: <[email protected]>
Reply-To: Richard Nute <[email protected]>
Subject: Re: [PSES] What's the deal with Wire Nuts?

>From the photo, I believe we see two wire nuts, the plastic cases of
which have fused together.  One wire nut connects the two black
(live) wires, and one wire nut connects the two white (neutral) wires.
(Note the smoke deposits on the white wires.)

A yellow wire nut is rated for minimum 2 #18 up to 4 #14.  So, I
suspect that each wire nut connects 2 #14 wires, where #14 is
the most common 120-V, 15-A wire.

I doubt the overheating resulted in a L-N short because such a short
would have resulted in arcing (no evidence) and burning of the
plastic, and considerably more overheating.  Of course, if such a
short did occur, then the overcurrent device operated quickly and
prevented further heating.

My hypothesis is that the two wire nuts were in contact with each
other.  And the load was quite high, resulting in heating of the
contact resistance in both wire nuts.  The plastic melted, the two
nuts fused together, and the wires touched.  Since the load was
already quite high, the overcurrent device  was near its operating
current, and the overcurrent device operated quickly before any
further damage was done.

Other hypotheses?

I wouldn't blackball wire nuts.  My house has lots of wire nuts
in its electrical installation;  no failures after 25 years!


Best regards,
Rich





-----Original Message----- 
From: Schaefer, David
Sent: Tuesday, October 09, 2012 6:11 AM
To: [email protected]
Subject: Re: [PSES] What's the deal with Wire Nuts?

After pulling this out of a piece of equipment, I have serious doubts about 
the long term use of wire nuts.

http://s139.photobucket.com/albums/q296/user8888/?action=view&current=2012-10-08185745.jpg


David Schaefer
Senior EMC Engineer
TÜV SÜD America Inc
Office: 651 638 0251
Cell: 612 578 6038
Fax: 651 638 0285




-----Original Message-----
From: Doug Powell [mailto:[email protected]]
Sent: Monday, October 08, 2012 10:45 AM
To: [email protected]
Subject: [PSES] What's the deal with Wire Nuts?

At the risk of redundancy, I would like to re-open a question from
2008 "What's the deal with Wire Nuts?"
http://www.mail-archive.com/[email protected]/msg56599.html

The original discussion seems to track well with my own opinion on the use 
of these wiring devices, but this is based my opinion.  I am aware of many 
American appliance manufacturers who use these devices and still obtain 
their safety certifications.  It is my *opinion* that any equipment destined 
for the European market should not use these devices but I cannot find any 
direct prohibition on their use.  The IPC 620 standard may have limits but 
this is more like a workmanship standard.

Several reasons might be used to prohibit their use:

1) Temperature ratings
2) Secondary securement of conductors
3) Insufficient coverage of bare metal parts and resulting electrical tape 
used (creepage problem)
4) No limit to the number of conductors
5) Over/Under twisting of the connector
6) Metallic insert or non-metallic


This time around my context is equipment that falls under the scope of IEC 
61010-1 and its derivatives.  Has anyone seen a definitive answer to this 
question?

--
Thanks, -doug

Douglas E Powell
[email protected]
http://www.linkedin.com/in/dougp01

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to