I really appreciate everyone who commented on this topic.

I should have mentioned that our products are generally not certified by a 
national authority so they are subject to Field Inspections where the 
inspecting engineer doesn't always have the ability to perform fault testing on 
site. So generally they have to consider the ratings of the components, 
supplementary OCPD, and branch circuit protection during their evaluation.

Products that draw current between 10 amps and 20 amps using the IEC connectors 
have always confused me as far as protecting the connector.

Another example, in one product we have a small ac line filter rated 3 amps 
(which filters only one of many circuits inside our device). The CSA engineer 
told us that though this part is rated 3 amps (functional), it is certified to 
be safe when connected to a 15 amp branch circuit. However when used in a 
product that requires a 30 amp branch circuit, internally we had to add a 15 
amp Supplementary OCPD to protect the filter. The same goes with AC cooling 
fans.

So what a part is rated and how it is protected is often not clear to me.

Thanks again.
The Other Brian

-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf Of Ted Eckert
Sent: Wednesday, November 21, 2012 12:13 PM
To: [email protected]
Subject: RE: IEC 60320 C13/C14 Connector 10A vs 15A

Hello Brian,

Whether or not there is a requirements for supplementary overcurrent protection 
depends on the product classification and applicable safety standard. In 
general, supplementary overcurrent protection is not required. For example, in 
IEC 60950-1, the product still needs to pass abnormal condition and component 
fault tests. However, if it can do so while depending only on the branch 
circuit protection, it is considered to meet the requirements.

In practice, supplementary overcurrent protection is often one of the easiest 
ways to meet the compliance requirements. Without the supplementary protection, 
other components in the circuit may need to be oversized to handle the large 
available fault currents off of a branch circuit.

Ted Eckert
Compliance Engineer
Microsoft Corporation
[email protected]

The opinions expressed are my own and do not necessarily reflect those of my 
employer.
-----Original Message-----
From: Kunde, Brian [mailto:[email protected]]
Sent: Tuesday, November 20, 2012 9:28 AM
To: [email protected]
Subject: Re: IEC 60320 C13/C14 Connector 10A vs 15A

Even though these connectors are rated less than the branch circuit they are 
powered by, don't you have to have supplemental over current protection within 
the device rated at or below the rating of the connector to protect the 
connector?

I'll explain my case again.

Device operating at 115VAC in North America using an IEC connector rated 15 
amps, powered by a 15 amp branch circuit, drawing and rated 12 amps with a 12 
amp over current protection device.

But, when this product is used in Europe, it operates at 230VAC, now the same 
IEC connector is rated 10 amps, powered by a 16 amp branch circuit, it draws 
and is rated only 6 amps, but still has the 12 amp over current protection 
device.

Logic dictates that this would be a problem and that the over current 
protection device would have to be changed to a lower value (something below 10 
amps).

Am I thinking right or is there some exclusion where IEC C13/C14 connectors can 
handle the fault current from a 16 amps branch circuit in Europe?

Thanks,
Brian

-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf Of Peter Tarver
Sent: Tuesday, November 20, 2012 12:13 PM
To: [email protected]
Subject: RE: [PSES] IEC 60320 C13/C14 Connector 10A vs 15A

Brian -

I've seen IEC 60320 C13/C14 appliance couplers/inlets marked as rated for less 
than 10 A for use in N.A.  I have also seen N.A. cordsets using the
C14 coupler rated as low as 7 A.  Caveat emptor.

I have also owned small appliances using the IEC 60320 C1/C2 couplers/inlets 
(0.2 A) coupler with a 1-15P attachment plug.

The C5/C6 couplers/inlets are very common for use with laptop computers having 
5-15P attachment plug.

Ted's comments apply.


Peter Tarver


This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>
________________________________

LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>
________________________________

LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to