Gentlemen:
Please recall that Ethernet is isolated from the sender/receiver circuits at each end of the Ethernet circuit (where the isolation in the equipment usually is a part of the Ethernet RJ45 connector). The isolation is 1500 V rms. Why? Because building transients magnetically couple into the Ethernet cable within the building wiring. Consider two buildings. The NEC requires the neutral to be grounded at each building service entrance. Therefore, the neutral is grounded at two points, which places the ground in parallel with the neutral, and, VOILA! the ground between the two buildings is a current-carrying conductor. Isolation from ground is required because, otherwise, the Ethernet conductors would be in parallel with the ground and would become a third current carrying conductor between the two buildings. And would quickly open due to the current. As I understand POE... http://hw-server.com/images/supply_diagram.png POE is a common-mode circuit between two Ethernet pair conductors. As shown in the diagram, the "powered device" must have a DC-DC converter which is isolated from ground (again, 1500 V RMS). http://www.poweroverethernet.com/associated/files/file_334_1114621476.pdf POE is a maximum 48 V DC. This circuit comprises SELV between poles, and a Limited Current Circuit between each pole and ground. The Ethernet standards require isolation between: (1) the Ethernet circuits and the internal equipment circuits (provided by the RJ45) and (2) the DC-DC converter input and output (provided by the equipment). However, 60950-1 does not require clearance or creepage across these isolations. Best regards, Rich -----Original Message----- From: Bill Owsley Sent: Monday, November 26, 2012 5:48 PM To: ralph.mcdiar...@schneider-electric.com ; EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] POE creepage & clearances SELV is 60 vdc but not if outdoor or wet environment - right ??? Then it drops to 30 vdc? So Ethernet is inside only for easy compliance ?? Maybe one can extend the inside environment to an outside application by careful use and implementation of conduit and enclosures... We get lazy and apply the creepage and clearance and keep moving. ps. I am not a safety engineer and have no clue... I suspect that the 1500 v isolation came from a single fault introduced at the PoE injector that tied primary to secondary and thus the PoE device needed to also have the isolation to withstand that fault. Add up how many isolation transformers are in the circuits back to primary and/or TNV-1. From: "ralph.mcdiar...@schneider-electric.com" <ralph.mcdiar...@schneider-electric.com> To: EMC-PSTC@LISTSERV.IEEE.ORG Sent: Monday, November 26, 2012 7:21 PM Subject: Re: [PSES] POE creepage & clearances The external DC power supply needs to be SELV too, not just energy limited. _______________________________________________________________________________ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA | Regulatory Compliance Engineering From: Ron Pickard <rpick...@equinoxpayments.com> To: EMC-PSTC@LISTSERV.IEEE.ORG, Date: 11/26/2012 12:38 PM Subject: Re: [PSES] POE creepage & clearances Hi Joe, I agree that an Ethernet circuit would be considered to be an SELV circuit and that would be true if the POE circuit were completely on premise generally, which would categorize this as a Class III product according to IEC/UL 60950-1 2nd Ed. given that the external power supply is a limited power source (LPS). However, TNV-1 creepage/clearance requirements would apply if the POE were to be exposed to overvoltages from telecommunication networks (essentially off premise) requiring Basic insulation. I make this distinction as Ian did not mention where the POE circuit originates. Best regards, Ron From: Joe Randolph [mailto:j...@randolph-telecom.com] Sent: Monday, November 26, 2012 12:43 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] POE creepage & clearances Hi Ian: I think the short answer to your question is that under 60950 there are no requirements for creepage and clearance distance between the Ethernet circuit and ordinary SELV circuits that are user-contactable. This is because under 60950, Ethernet is classified as an SELV circuit. There are no requirements to separate one SELV circuit from another. Where this issue becomes confusing is that under the Ethernet 802.3 standard, an Ethernet port must provide a 1500 VRMS isolation barrier between the Ethernet conductors and earth. This is a legacy requirement whose origins seem to have been lost in the sands of time. However, I believe the consensus view is that the original intent of this requirement was to protect against ground loops and was not related to user safety. Nevertheless, the 802.3 isolation requirement has sometimes been treated as though it is a safety requirement. Note that the 802.3 requirement is for a simple dielectric test, with no reference to creepage, clearance, or distance through solid insulation. So, in principle, there are no safety isolation requirements for your application, since both of the proposed power supplies have a SELV output. This makes the entire device a SELV circuit (unless there are other ports on the device that are not SELV). Joe Randolph Telecom Design Consultant Randolph Telecom, Inc. 781-721-2848 (USA) j...@randolph-telecom.com http://www.randolph-telecom.com - ---------------------------------------------------------------- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://listserv.ieee.org/request/user-guide.html List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <emcp...@radiusnorth.net> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>