Hi Joe:

Sorry for the delay in my reply to your questions.

SPDs are used on mains circuits, both between the
poles and poles to earth.  In this latter application,
the SPD is in parallel with basic insulation.

SPDs are also used on low-voltage external circuits
that are subject to transient over-voltages such as
antenna circuits and telephone circuits.  The SPDs
are between the external circuit and earth, or
between the external circuit and the mains circuit.
In this latter case, for the purposes of a transient
over-voltage originating in the external circuit,
the mains circuit is a connection to earth.

Usually, within the equipment, these external
circuits are isolated from earth and from equipment
secondary circuits.  Indeed, the standards require
such isolation (to protect personnel touching such
circuits downstream from the equipment).

But, because these circuits are low voltage, the
isolation system is not a safety isolation, i.e, is
not a basic insulation.

Nevertheless, because the external circuits are
subject to transient over-voltages, the isolation
system must withstand such over-voltages.  Therefore,
the isolation system is subject to an electric
strength test.  And, the isolation system can be
bridged by an SPD at the discretion of the designer.

The principle I described in my previous message on
this subject applies here.  In the case of an open-
circuit failure of the SPD, the external circuit
isolation system must withstand the expected
transient over-voltages.  Hence, a separate voltage-
withstand test of the isolation system without the
SPD.

While the equipment is not required to have reliable
earth, many of the requirements are excluded if the
equipment does have reliable earth.

The standard does not address the short-circuit or
low-resistance failure of an SPD that is connected
between the external circuit and the mains.
However, external circuits are normally isolated
from earth, so no transient current can flow in the
reverse direction, i.e., from mains to the external
circuit.

I suppose the SPD can bridge the isolation, i.e.,
from external circuit to secondary circuit.  If
the secondary circuit is connected to earth, then
the SPD simply conducts to earth.  If the secondary
circuit is not earthed, then the SPD conducts
through the primary-secondary capacitance to the
mains.

Further questions or objections?


Best regards,
Rich

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@radiusnorth.net>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to