Rich,
Given your rational that surge protective components
(SPCs), such as MOVs or GDTs, can have a fault mode anywhere
between a short-circuit and an open-circuit, looks like
there is a disconnect in the test levels.
In the open-circuit situation, the SPC does not divert
current and the full voltage is applied to the electrical
insulation. That being the case and as TC 108 specifies MOVs
are tested with a impulse generator voltage of 6 kV peak,
why isn't the insulation tested with this 6 kV impulse?
Regards
Mick.
On 20/05/2013 22:50, Richard Nute wrote:
Hi Joe:
Very quickly...
SPDs are not considered reliable components or assemblies.
The safety standards anticipate a failure -- anywhere from
open-circuit to short-circuit.
In the event of an open-circuit, there is no indication of
such a failure. And, of course, all transients then pass
through the open SPD.
Consequently, the equipment safety insulations will be
called upon to withstand the expected transient overvoltages.
So, the standards require performing the voltage withstand
test without the SPD in place.
Best regards,
Rich
On 5/20/2013 1:40 PM, Joe Randolph wrote:
Hi Rich:
I'm hoping that you can provide one of your
straightforward "Rich Nute Explanations" for the apparent
contradiction behind the rationale that allows a surge
protection component to be placed across a required
safety isolation barrier, and then removed for the
purpose of performing the hipot test.
I have been involved with safety compliance for over 30
years, and this concept is one that has never made
complete sense to me. On one level, I can just bump
along and limit my attention to what the safety standard
actually says, but I would like to understand what the
thinking is behind that.
This allowance (removing surge protection components for
the hipot test) appears in a variety of standards and
clauses within those standards, such as EN 60950-1,
clauses 5.2.2, 6.1.2, and 6.2.2.
If you could help clarify the thinking behind this
allowance, I would greatly appreciate it.
Thanks,
Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
[email protected]
http://www.randolph-telecom.com
<http://www.randolph-telecom.com/>
Hi Bill:
SPDs, regardless of configuration, are notorious for being
prone to failure, either short-circuit or open-circuit or
any value of resistance between those two extremes. (One
cannot predict the energy the SPD will be required to
dissipate.)
From a safety point of view, all such failures must be
accounted for such that the safety of the equipment is not
compromised by any failure of the SPD.
If the SPD should fail open-circuit, then expected
transients that are therefore not attenuated, must not
cause the insulation to fail. Hence, the insulation must
pass the hi-pot test without the SPD in place.
As for the requirement for the GDT to pass the hi-pot
test...
??? I don't have any rationale for this.
Best regards,
Rich
On 5/10/2013 10:11 AM, Bill Owsley wrote:
I'm running into a dilemma. Not being a Safety
Engineer myself, but rubbing elbows with them...
On a piece of ITE equipment, I need some surge
suppression for worldwide markets with one annoying
requirement for 4 kV, otherwise just 2 kV line to
earth, and using either plugable cords or permanent
connection, whichever is worse.
Now the Safety guys tell me that MOV's alone cannot
bridge the insulation (Basic or Functional, I forget.)
between primary and earth, when using one of power
cable options mentioned above.
But a proper qualified (GDT) gas discharge tube can do
the bridging. So we figured to use them in series.
On a quick and dirty bench test it works to 4 kV.
Then the Safety guys pull out the rest of the story and
point out 5.2.2 which seems to indicate that the GDT is
to meet the Hi-Pot test, 1500 vac.
Previously, section, 1.5.9.4 (?) indicates that the
surge protection devices can be removed during the
Hi-Pot test.
But now I have a Surge suppression circuit that has to
withstand the same Hi-Pot as the rest of the board.
Question is how does a surge protection circuit protect
the board when it has to meet the same Hi-Pot test?
In other words, when a surge comes along, which is
going to break over first?
The surge protection or the board?
Is the purpose of surge suppression is to keep the
clamped voltage below a problem level?
What am I missing in this?
Thanks...
- Bill
-
----------------------------------------------------------------
This message is from the IEEE Product Safety
Engineering Society emc-pstc discussion list. To post a
message to the list, send your e-mail to
<[email protected] <mailto:[email protected]>>
All emc-pstc postings are archived and searchable on
the web at: http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online
Communities site at
http://product-compliance.oc.ieee.org/ can be used for
graphics (in well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions:
http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]
<mailto:[email protected]>>
Mike Cantwell <[email protected]
<mailto:[email protected]>>
For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]>>
David Heald <[email protected] <mailto:[email protected]>>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering
Society emc-pstc discussion list. To post a message to
the list, send your e-mail to <[email protected]>
All emc-pstc postings are archived and searchable on the
web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online
Communities site at
http://product-compliance.oc.ieee.org/ can be used for
graphics (in well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions:
http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>
For policy questions, send mail to:
Jim Bacher: <[email protected]>
David Heald: <[email protected]>
Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
[email protected]
http://www.randolph-telecom.com
<http://www.randolph-telecom.com/>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering
Society emc-pstc discussion list. To post a message to the
list, send your e-mail to <[email protected]>
All emc-pstc postings are archived and searchable on the
web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online
Communities site at http://product-compliance.oc.ieee.org/
can be used for graphics (in well-used formats), large
files, etc.
Website: http://www.ieee-pses.org/
Instructions:
http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>
For policy questions, send mail to:
Jim Bacher: <[email protected]>
David Heald: <[email protected]>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion
list. To post a message to the list, send your e-mail to <[email protected]>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>
For policy questions, send mail to:
Jim Bacher: <[email protected]>
David Heald: <[email protected]>