Brian,
How is the furnace shut off?  If you are using a contactor between the
main line filter and the furnace, a phase line might open when it is
carrying high current.  The inductance of the line filter will try to
keep this current flowing, generating a very-high kickback spike at the
*output* of the line filter.  

Or, since the contacts in the contactor are unlikely to open/close at
exactly the same time, a common-mode choke in the line filter can act as
a transformer putting noise on the open phase(s) if only 1 or 2 phases
are connected to the load.  Some years ago, Bill Kimmel and Daryl Gerke
wrote about a case where a 3-phase product had a contactor between a
line filter and the load, which generated horrendous Conducted Emissions
noise every time the contactor opened or closed, because of this
transformer action.  The solution was to replace the common-mode choke
with 3 separate chokes, one for each phase line.

John Barnes KS4GL, PE, NCE, NCT, ESDC Eng, ESDC Tech, PSE, Master EMC  
  Design Eng, SM IEEE (retired)
Lexington, KY
http://www.dbicorporation.com/

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to