Doug,

I am not an official UL person but based on my experience of working on 
this standard , i saw some information for this test requirement.

Yes, there is a provision for Hydrostatic test at recent version of 
UL61800-5-1 under 5.2.7 (Type test and production routine test).

 Requirement for type test  is 2 times the operating value or 1.5 times 
the maximum pressure rating of the device whichever is the greater 
pressure for 1 minute. For routine or production test , pressure needs to 
increase at its operating value for 1 minute. 

There is 4.4.5.2.4 Leakage of coolant section and 4.4.5.2.4DV (also 
4.5.2.2) talks about pressure relief mechanism and cooling system 
requirement to satisfy the test requirement.

By the way, Feb.1st of  2016 was the last day to evaluate new products 
under 508C (correct me if i am wrong). Can we open the file and update 
ratings that required test using 508C if needed after this Feb.1st 
deadline ?

Hope it helps!

Thank you.

Best regards,

Binayak Marahatta
Product Compliance Engineer

www.kebamerica.com
Email: 
[email protected]
Phone: 
Main Phone:  952-224-1400 Ext. 1458
Linkedin:
https://www.linkedin.com/company/keb-america-inc
Google+:
www.google.com/+KEBAmericaInc
------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
-------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
KEB products are Control Technology, Inverters, Converters,Elevator 
Controllers, Servo systems, Frequency generators, Communication, EMC 
Products,  Motor,most economical  low and high torque brakes, Dynamic or 
static breaking, Fail-safe Brake, Combistop (Spring Applied brakes,Power 
off, fail safe  & High Torque Brake), Combiperm (Permanent magnet  Brake 
or Clutch, Power-off Brake), Combinorm (Power-on Brakes,Brake and /or 
Clutches), Combibox ( Enclosed Clutch and /or Brake, Combinorm Clutch and 
Combiperm Brake),C-Face brakes  and Gears, Elevator Technology, Medical 
Technology, Material Technology, Automotive,Magnetic Technology etc.

Note: KEB has production sites, marketing companies and representations in 
more than 20+ countries. 
-----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------

This e-mail, and any attachment to it, contains confidential information 
that may be legally privileged and which is intended only for the 
addressee(s) named above. Any use by an unintended recipient is strictly 
prohibited. If you have received this e-mail in error, please contact the 
sender and delete it from your system.
"Just my opinion/ statement PSES, it isn't from my company's official 
statement"



From:   Doug Powell <[email protected]>
To:     [email protected], 
Date:   02/01/2016 05:37 PM
Subject:        Re: [PSES] UL 508C transition to UL 61800-5-1



All,

In reviewing the details it is possible the UL committee followed the IEC 
standard a little closer than I had thought.  The table of contents at 
http://ulstandards.ul.com/standard/?id=61800-5-1_1 has no indicaiton of 
such a test but the IEC versoin of teh standard has clause 5.2.7 for 
hydrostatic test.  the UL standard seems to skip over this.  It seems a 
bit crazy the committee would toss out whole sections and then call the 
standard harmonized.

Thanks,  Doug




On Mon, Feb 1, 2016 at 4:18 PM, Doug Powell <[email protected]> wrote:
All,

I am presently working with a 10 MW inverter that uses water cooling.  In 
the past, the UL inspector has said we should use sections from UL 508C - 
67.1 Loss of cooling medium circulation test  & 67.2 Hydrostatic pressure 
test.  The new UL 61800-5-1 has no such provisions.  I did a little 
research and my first thought was to look into UL 1012 which is also used 
for some types of industrial power conversion equipment, but it was of no 
help.  I looked into UL 61010-1 and the fluid containing parts section 
seems possible but using a laboratory equipment standard for a 10 MW 
inverter seems a bit out of line. The original tests in 508C could be used 
but it is being withdrawn from use this month.  

Has anyone faced this problem and found an acceptable solution?

​thanks, Doug

​


-- 

Douglas E Powell

[email protected]
http://www.linkedin.com/in/dougp01
ᐧ



-- 

Douglas E Powell

[email protected]
http://www.linkedin.com/in/dougp01
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to <
[email protected]>
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in 
well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 
For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to