On one conductor, cm and dm sum, and on the other, they subtract. If a sum
and difference of two quantities is equal, it can only be because one of
them is zero (or much less than the other).

Ken Javor
Ph. (256) 650-5261 




From: Elliott Martinson <[email protected]>
Date: Tue, 29 Mar 2016 21:37:42 +0000
To: Ken Javor <[email protected]>, "[email protected]"
<[email protected]>
Conversation: [PSES] Commom mode current vs. differential mode current and
LISN
Subject: RE: [PSES] Commom mode current vs. differential mode current and
LISN

The LISNMARK (LISN MATE) is exactly the same device as what I linked to.
 
As for the current probes, comparing L and N to determine if one of cm or dm
predominatesŠ we are talking about noise signals, and measuring magnitudes
(no phase info) in frequency domain, right? I know that on one conductor,
you can say CM/DM add while they subtract on the other (mathematically
correct no matter which you call L and which you call N). I¹m confused at
how you know it cannot be similar amounts CM and DM noise when the noise
magnitude is the same between L and N. I¹d appreciate it if you could
explain.
 
Obviously running L+N simultaneously through the same probe gives
common-mode noise, I¹m not sure if I worded my response badly because I
meant to say bullet #3 is completely correct (as is 1, along with 4 assuming
no ³LISNMATE²)
 

Elliott Martinson
Product Assurance Specialist I
Electronic Theatre Controls
3031 N PLEASANT VIEW RD
MIDDLETON WI 53562-4809
Work: 608.824.5696 / Cell: 608.209.9897
[email protected] <[email protected]>
 

From: Ken Javor [mailto:[email protected]]
Sent: Tuesday, March 29, 2016 4:14 PM
To: [email protected]
Subject: Re: [PSES] Commom mode current vs. differential mode current and
LISN
 
Disagree. Westin had it right. A current probe can be used to isolate either
cm or dm current. If at any frequency the signal amplitude on individual
line and neutral conductors are very close, then all you can say is that at
that frequency either cm or dm predominates, but you can¹t say which.  With
a LISN, a separate device must be used. Mark Nave of EMC Services designed a
three port device (connects to each LISN port and to the EMI receiver)
trademarked LISNMATE in the 1980s to isolate common mode, and sometime later
he produced LISNMARK, which isolated DM.  Within the past decade, Ray Adams
while at Fischer Custom Communications packed both functions in one piece of
equipment, which if memory serves was named LISNUP.

EMC Services, Mark Nave¹s company, is no longer producing his products, but
I believe the FCC product is still available.

Ken Javor
Ph. (256) 650-5261 



From: Elliott Martinson <[email protected]>
Reply-To: Elliott Martinson <[email protected]>
Date: Tue, 29 Mar 2016 20:36:18 +0000
To: <[email protected]>
Conversation: [PSES] Commom mode current vs. differential mode current and
LISN
Subject: Re: [PSES] Commom mode current vs. differential mode current and
LISN

http://www.hottconsultants.com/techtips/CM_vs_DM%20Conducted_Emission.html
This is a great resource for your question.
 
Your second point kind of contradicts your first, if it¹s trying to say what
I think it is. DM and CM each show up on L, but the same is true for N. It¹s
a linear combination of both, so even if L and N are almost equal, you can¹t
say anything about the proportion of DM to CM currents.
 
If they are not equal, then this implies current is travelling back via the
ground conductor and/or energy¹s being lost to radiated emissions.
 
What you need is a physical circuit to do the adding/subtracting of the LISN
outputs. (otherwise your 3rd bullet point is correct)
 
Your 4th bullet, well I refer you to the link above.
 

Elliott Martinson
Product Assurance Specialist I
Electronic Theatre Controls
3031 N PLEASANT VIEW RD
MIDDLETON WI 53562-4809
Work: 608.824.5696 / Cell: 608.209.9897
[email protected] <[email protected]>
 

From: Amund Westin [mailto:[email protected]]
Sent: Tuesday, March 29, 2016 1:23 PM
To: [email protected]
Subject: [PSES] Commom mode current vs. differential mode current and LISN

Please correct me, if I am wrong (that happens quite often Š):

·        Let one wire (L) pass through a current clamp, and you measure the
combination of current mode and differential mode currents

·        Do the same with wire N. If L and N are (almost) equal, you either
have major part of DM currents or major part of CM current

·        Let both wire (L and N) pass through a current clamp, and you
measure the only CM current (DM is canceled)

·         When doing conducted emission test by LISN, you actually get what
you get. LISN do not see the difference between CM or DM. From LISN
measurements, you can¹t say if noise is CM or DM.

B.regards

Amund













-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website:      http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html>
List rules:     http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher  <[email protected]>
David Heald <[email protected]>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]>



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to