The United States has significant national differences.

Many U.S. national standards have very strict flammability requirement for 
larger areas of materials used indoors. The basic requirement applies when you 
have a piece of material longer than 6 feet (2 meters) or greater than 10 
square feet (1 square meter) in area. This material must pass the Steiner Fire 
Tunnel test, covered in ASTM E84 and UL 723. This video gives a basic outline 
of the test<https://www.youtube.com/watch?time_continue=1&v=iEe5dQ7LPhM>. 
Interior building surfaces must meet fairly strict requirements and this would 
include a large sheet of plastic on the back of a refrigerator. There are even 
stricter requirements for materials used in air plenums, such as above a 
suspended ceiling.

The linked video references the “International Building Code”, or the IBC. The 
same requirements are in the Uniform Building Code, or UBC. Most municipalities 
in the United States adopt either the IBC or UBC.

Here is a sample UL Listing for a material commonly used for kitchen 
countertops<http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name=BTAT.R11986&ccnshorttitle=Molded+Plastic&objid=1074291935&cfgid=1073741824&version=versionless&parent_id=1073984739&sequence=1>.
 Similar requirements apply to drywall, flooring materials, plastic glazing 
materials, ceiling tiles and other construction products.

Many U.S. national standards do not specifically call out this requirement, 
largely because few products that fall under those standards have enough 
surface area. For example, I had a large piece of computer equipment certified 
to UL 60950-1. UL applied the UL 723 requirements to the plastics used for 
large air plenums on the structure. It was probably one of the few pieces of 
ITE equipment I’ve ever seen with pieces of plastic large enough to warrant UL 
723 testing.

The back of a refrigerator would be close to the limits where a U.S. Nationally 
Recognized Test Laboratory (NRTL) might apply UL 723. The refrigerator 
manufacturer could come up with ways of reducing the panel size below the limit 
to avoid this challenging test.

The Steiner Tunnel Test is also used for wiring that could be hidden in walls 
or air plenums, such as above a suspended ceiling. There is another U.S. 
national difference that affects wires over 10 feet (3.05 meters) in length. 
This is in UL 60950-1 and UL 62368-1. If your computer’s external cable is less 
than 3.05 m, it only needs to be VW-1, FT-1 or better. If the cable is longer, 
there is a concern that it could carry flame from where the computer is located 
to another occupied space. Finding an Ethernet cable that meets this 
requirement, often called plenum rated, is easy. Finding a USB cable that meets 
the requirement is hard.

Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my 
employer, any NRTL or the code authorities behind the IBC and UBC.



From: Scott Xe [mailto:[email protected]]
Sent: Sunday, June 25, 2017 7:01 AM
To: [email protected]
Subject: Re: [PSES] Metal back of US fridge - Grenfell Tower Fire

Adam,

It is a good statistics!

Actually US now also adopts UL EN 60335-2-24 as their safety standard.  Does UL 
have deviation for US in this standard as suggested by John?

Thanks and regards,

Scott

From: Adam Dixon <[email protected]<mailto:[email protected]>>
Reply-To: Adam Dixon 
<[email protected]<mailto:[email protected]>>
Date: Sunday, 25 June 2017 at 7:52 PM
To: <[email protected]<mailto:[email protected]>>
Subject: Re: [PSES] Metal back of US fridge - Grenfell Tower Fire

Here's another good UK data source for incidents, not recalls:

https://www.gov.uk/government/statistical-data-sets/fire-statistics-data-tables<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.gov.uk%2Fgovernment%2Fstatistical-data-sets%2Ffire-statistics-data-tables&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165781837&sdata=FwqZC6%2BVF27OkRORXGTemSPoSXe5YpSxkdHu9FarxkU%3D&reserved=0>

The "Domestic appliance fires dataset" file near the bottom can be parsed by 
appliance type.
Cheers,
Adam
[email protected]<mailto:[email protected]>


On Sun, Jun 25, 2017 at 7:42 AM, John Allen 
<[email protected]<mailto:[email protected]>>
 wrote:
Scott

Look on the EU Commission RAPEX site:
http://ec.europa.eu/consumers/consumers_safety/safety_products/rapex/alerts/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fec.europa.eu%2Fconsumers%2Fconsumers_safety%2Fsafety_products%2Frapex%2Falerts%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165791839&sdata=B%2BpZYmERccXhKqUrO3Y9ZaRzTspq9nj7Y6xqrhJ9mJs%3D&reserved=0>

Actually, don’t if you want to sleep tonight!

John E Allen
W.London, UK

From: Scott Xe [mailto:[email protected]<mailto:[email protected]>]
Sent: 25 June 2017 12:34
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] Metal back of US fridge - Grenfell Tower Fire

Hi Adam,

The info supplied is interesting!  Yes, it aligns with John’s thought.  
However, the recalled units are quite different – 5,200 vs 1.2 m.  In the UK, 
there are a few million recalls of clothes dryers in last few years – that is 
quite different from US data.  Is there similar data of UK and/or EU?

Cheers,

Scott


From: Adam Dixon <[email protected]<mailto:[email protected]>>
Date: Sunday, 25 June 2017 at 7:06 PM
To: Scott Xe <[email protected]<mailto:[email protected]>>, 
<[email protected]<mailto:[email protected]>>
Cc: <[email protected]<mailto:[email protected]>>
Subject: Re: [PSES] Metal back of US fridge - Grenfell Tower Fire

Here's a slightly dated but popular US magazine article with a table near the 
end that supports John's closing thought about rarity of fridge fires compared 
to tumble-dryer fires (1:9 ratio).

http://www.consumerreports.org/cro/magazine/2012/03/appliance-fires-is-your-home-safe/index.htm<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.consumerreports.org%2Fcro%2Fmagazine%2F2012%2F03%2Fappliance-fires-is-your-home-safe%2Findex.htm&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165791839&sdata=aEnwHYkLu9GrByivxXoHMtluDF3ExAoDloWIrPrhtT0%3D&reserved=0>
Cheers,
Adam
[email protected]<mailto:[email protected]>


On Sun, Jun 25, 2017 at 6:52 AM, Scott Xe 
<[email protected]<mailto:[email protected]>> wrote:
John, thanks for background info!

LFB said one fire every day in London is caused by white goods.  It is a 
horrible figure!

Grenfell Tower Fire is a bit different from previous ones and had another risk 
of non-approved insulation and cladding tiles on the outer wall of building.  
It is still unclear how the fire spreads from the fridge to the cladding 
titles.  Was the fridge close to the windows?

From the video, the metal back seems to work delaying the fire spread.  It may 
trigger the standard body to think it again.  The capacitor incident prevention 
has been incorporated into the safety standard, why not this one?  LFB may take 
this case to reinforce their warning alert in 2015.

Scott

On 25/6/2017, 5:25 PM, "John Woodgate" 
<[email protected]<mailto:[email protected]>> wrote:

    It's not quite 'resistance', it's more a matter of different priorities. US 
safety standards major on protection against fire because they were originated 
by the insurance industry (Underwriters Laboratory) for obvious financial 
reasons, while European  safety standards major on prevention of electric 
shock, because 230 V is more dangerous than 120 V (but of course not more 
dangerous than 240 V!), and timber-framed buildings are relatively rare in 
Europe.

    I guess that the applicable safety standard (IEC/EN 60335-2-xxx)  isn't 
strongly influenced by US experts (US may even have voted for it) and thus 
doesn’t require a metal back panel, whereas the UL standard (which may be the 
IEC standard with a modification or several) does require one.

    All the Sections of IEC 60335-2 are under continuous review as technologies 
change, and the recent incidence of fires may well result in significant 
changes.

    However, unlike the tumble dryer case, where numerous fires were reported, 
this fridge-freezer fire is just one incident, and may be due to a 'one-off' 
fault' or obstruction of the ventilation. Even the enquiry that is being held 
may not be able to assign a definite cause. I suspect that fridge fires are 
very much rarer than tumble-dryer fires, even if, to be fair, the epidemic 
dryer fires are excluded.

    With best wishes DESIGN IT IN! OOO – Own Opinions Only
    
www.jmwa.demon.co.uk<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.jmwa.demon.co.uk&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165791839&sdata=ewI3pMv%2B%2FSyeNkkneh8bgtWX9oIKUIFhhvmVkXHD3hs%3D&reserved=0>
 J M Woodgate and Associates Rayleigh England

    Sylvae in aeternum manent.

    -----Original Message-----
    From: Scott Xe 
[mailto:[email protected]<mailto:scott.xe@G-%3cBR%3e----------------------------------------------------------------%3cBR%3e%3cp%3eThis%20message%20is%20from%20the%20IEEE%20Product%20Safety%20Engineering%20Society%20emc-pstc%20discussion%20list.%20To%20post%20a%20message%20to%20the%20list,%20send%20your%20e-mail%20to%20%3c%3cA%20HREF=>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165791839&sdata=l1RnVJPaZ6DrDl8Sre2WZZHPWJ8bntqXq6SyKancp5k%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165791839&sdata=euJOUZgEen4mFMgZVsDDNGMyjeHtbPB0NszZObsL8Ls%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165791839&sdata=7OJQKHvMsmpDz2nii0JICMCFmQ5Mw5TJuekMdXrg6bk%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165791839&sdata=Oh0VetogpAIPGPGSFZZq19mOJoWM0vh1EqUOel56%2B4I%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165791839&sdata=ebZpPH8QshSN1PJtrWBf83RxlRCXUx1lSYqSQzJ2N%2Fw%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165791839&sdata=l1RnVJPaZ6DrDl8Sre2WZZHPWJ8bntqXq6SyKancp5k%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165791839&sdata=euJOUZgEen4mFMgZVsDDNGMyjeHtbPB0NszZObsL8Ls%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165801847&sdata=W2Lx2EWCz%2FHvqg%2BHST7h40rWLXUvrxDQL3izWaoPySM%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165801847&sdata=lVSYHYy8KSTE5cQnmrMotuiEPsUImQRT%2Be%2Fg72tGlV8%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C17744cf20f834e2c7cfd08d4bbd2bc15%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636339961165801847&sdata=odl5kZ1pLjoCIl5421o3VnZ8pRa3v5x23u8pgkrS5MI%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to