Not sure if your question is specific to NEC or not.  There are other 
standards, for example UL 508A that have similar rules that are not specific to 
circuit sizes.

And the rules are not all straight forward as they apply to conductor sizing, 
branch circuit protection, connectors/components, etc. and the type of loads.   
For example NFPA 70 210.20 (A) states  “Where a branch circuit supplies 
continuous loads or any combination of continuous and noncontinuous loads, the 
rating of the overcurrent device shall not be less than the noncontinuous load 
plus 125 percent of the continuous load.  Exception: Where the assembly, 
including the overcurrent devices protecting the branch circuit(s), is listed 
for operationat 100 percent of its rating, the ampere rating of the overcurrent 
device shall be permitted to be not less than the sum of the continuous load 
plus the noncontinuous load.” without mentioning anything about circuit size.

-Dave

From: Kunde, Brian [mailto:[email protected]]
Sent: Wednesday, October 11, 2017 3:02 PM
To: [email protected]
Subject: Re: [PSES] NEMA 5-20P with IEC 60320 C13

One last quick question, if I may, while we are all up on the NEC.

Just to confirm, the 80% rule only applies to 15A, 20A, and 30A branch 
circuits. 40A and 50A branch circuits do not have the 80% rule, even in a 
multiple-outlet configuration? I know these larger circuits are generally 
dedicated circuits, but that is how the rules read in the NEC 210.23(C). Unless 
I’m missing something.

Thanks bunches.
The Other Brian

From: John Woodgate [mailto:[email protected]]
Sent: Wednesday, October 11, 2017 2:57 PM
To: Kunde, Brian; [email protected]
Subject: Re: [PSES] NEMA 5-20P with IEC 60320 C13


Yes, of course quite a thin conductor will carry enough current to operate the 
protection, because it doesn't have time to get seriously hot.

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates www.woodjohn.uk<http://www.woodjohn.uk>

Rayleigh, Essex UK
On 2017-10-11 19:35, Kunde, Brian wrote:

I know I started this thread, so I'm going to circuit back via another 
direction.



The NEC allows a product with an 18 awg power cord (rated 10 amps), a 15 amp 
plug, and C13 IEC connector (15 amp) to be plugged into a 15 amp branch 
circuit. OH, you can also plug it into a 20 amp branch circuit because the 
receptacles will accept a 15 amp plug. So what protects the freakishly small 18 
awg power cord from bursting into flames in an overload condition?  Must be the 
OverCurrent Protection device in the product itself. Correct?



So back to original questions, can I use a power cord with a 20 amp plug (NEMA 
5-20P), 12 awg wire, and 15 amp IEC C13 connector on a product that draws 15 
amps and has a double pole 15 amp OCPD?  With the same logic above, the OCP 
device is protecting the power cord.



Would you allow this?  Then again, your you allow a 18awg power cord to be used 
on a 15 amp circuit?  The NEC says it is ok.



Thanks,

The Other Brian



-----Original Message-----

From: Nyffenegger, Dave [mailto:[email protected]]

Sent: Wednesday, October 11, 2017 1:30 PM

To: [email protected]<mailto:[email protected]>

Subject: Re: [PSES] NEMA 5-20P with IEC 60320 C13



Had a condo  with  a smallish through-the-wall A/C unit with NEMA 5-15P plug.  
In the room on one side of the unit was a dedicated 20A single outlet for the 
A/C unit.  In the room on the other side easily within reach of the cord was a 
standard duplex outlet on the room circuit.  Guess which one the A/C was 
plugged into?



-Dave



-----Original Message-----

From: Pete Perkins [mailto:[email protected]]

Sent: Wednesday, October 11, 2017 1:04 PM

To: [email protected]<mailto:[email protected]>

Subject: Re: [PSES] NEMA 5-20P with IEC 60320 C13



Ralph, Ted et al,



        Dunno how many times I have had this conversation with the project 
engineer who wants to use the full rated current from the duplex outlet (and 
not leave any for the other user who plugs into that outlet - which gives rise 
to the 80% rule) - except if they want to specify in the installation that the 
user must have an expensive electrician install a special dedicated outlet 
(only one plug available to the user on that CB controlled circuit); which 
gives rise to the marketing folks nixing the idea.  :>)    Carry on! As you 
were doing...



:>)     br,      Pete



Peter E Perkins, PE

Principal Product Safety & Regulatory Affairs Consultant PO Box 23427 Tigard, 
ORe  97281-3427



503/452-1201



[email protected]<mailto:[email protected]>



-----Original Message-----

From: Ralph McDiarmid [mailto:[email protected]]

Sent: Wednesday, October 11, 2017 9:05 AM

To: [email protected]<mailto:[email protected]>

Subject: Re: [PSES] NEMA 5-20P with IEC 60320 C13



Sounds like an example of the 125% rule for continuous (>3hr) current.  (20/16)



Ralph McDiarmid

Product Compliance

Engineering

Solar Business

Schneider Electric





From: Ted Eckert [mailto:[email protected]]

Sent: Wednesday, October 11, 2017 5:50 AM

To: [email protected]<mailto:[email protected]>

Subject: Re: [PSES] NEMA 5-20P with IEC 60320 C13



NFPA 70 allows 20 A connectors to be used at 20 A under a number of 
circumstances. The derating issue only applies in certain cases. Just changing 
the rating doesn’t resolve the issue as it would eliminate already accepted 
safe use of the connectors at their full rating.



Ted Eckert

Microsoft Corporation



The opinions expressed are my own and do not necessarily reflect those of my 
employer.



From: John Woodgate [mailto:[email protected]]

Sent: Tuesday, October 10, 2017 11:21 PM

To: Ted Eckert 
<mailto:[email protected]><mailto:[email protected]>; 
mailto:[email protected]

Subject: Re: [PSES] NEMA 5-20P with IEC 60320 C13



Yes, it could be difficult to change to respecting the rated values, so how 
about respecting the de-rated values instead? Instead of saying that you can 
only use this 20 A connector up to 16 A, call it a 16 A connector?

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.woodjohn.uk&data=02%7C01%7CTed.Eckert%40MICROSOFT.COM%7C6f5a4a13ae97469548f108d510703247%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432996434092831&sdata=vbIPUaUZRYojTmRGRu9LrQO4Emqy7f8wN1OY8mY%2BQFg%3D&reserved=0

Rayleigh, Essex UK

On 2017-10-10 21:57, Ted Eckert wrote:

The various clauses of NFPA 70 are reviewed, challenged, debated, argued and 
rewritten. I don’t think the clause in question remains because nobody has 
challenged it. Part of the issue is that the electrical infrastructure in the 
U.S. has been developed around this rule. If affects circuit breaker trip 
curves, conduit fill, wire sizes and rating and many other aspects of a 
building’s electrical system. If the rule were changed, would there be problems 
switching over? Would you have overheating in older structures where circuit 
breakers were replaced without updating wiring? Wold there be other effects of 
mixing 80% and 100% rated components? How many U.S. national standards would 
need to be updated?



It is a poor analogy, but think about switching sides that you drive on the 
road. Sweden switched on September 3, 1967. Street signs, traffic signals and 
road markings all had to be changed. Headlights had to be adjusted or re-aimed. 
For quite a while, there was a mix of left-hand and right-hand drive cars. It 
was a massive undertaking for a country with fewer people than either London or 
New York City.



Changing the way branch circuits are rated in the U.S. could be done, but it 
would be an extremely complicated undertaking. The risks of a mismatch of 
circuits, circuit protection and loads would be significant for a long time. I 
suspect that by the time the technology evolved to the point where the 
requirement could be eliminated, it was too late and eliminating it would 
result in too much expense and rework.



Ted Eckert

Microsoft Corporation



The opinions expressed are my own and do not necessarily reflect those of my 
employer.



From: John Woodgate [mailto:[email protected]]

Sent: Tuesday, October 10, 2017 12:49 PM

To: mailto:[email protected]

Subject: Re: [PSES] NEMA 5-20P with IEC 60320 C13



Well, yes, because the IEC tends to believe that rated values are realistic and 
do not need to be adjusted downwards. I suspect that at some point in the 
distant past (maybe even nearly 100 years ago), some connectors in wide use 
were found to overheat at rated current, so the 'derating rule' was brought in, 
and no-one has challenged it since.

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.woodjohn.uk&data=02%7C01%7Cted.eckert%40microsoft.com%7Cb9a5abba70d24e2f093e08d51018031b%7C72f988bf86f141af91ab2d7cd011db47%7C1%7C0%7C636432617679408094&sdata=jNpj%2FFhCHx9ir37o7Xf5GxovOe2h0nU9FIZnbo5mItE%3D&reserved=0

Rayleigh, Essex UK

On 2017-10-10 20:12, Ralph McDiarmid wrote:

The NEC (NFPA 70) talks about “continuous currents” and when to apply the 
all-too-familiar 125% rule.  Canadian Electric Code (CSA part I) has same 
requirement.  The IEC seems to have avoided it.



Ralph McDiarmid

Product Compliance

Engineering

Solar Business

Schneider Electric

D  604-422-2622



From: Kunde, Brian [mailto:[email protected]]

Sent: Monday, October 09, 2017 8:31 AM

To: mailto:[email protected]

Subject: [PSES] NEMA 5-20P with IEC 60320 C13



It is my understanding that according to the US National Electric Code, 15 amp 
receptacle are derated to 12 amps max., and 20 amp receptacles are derated to 
16 amps.



IEC 60320 C13 connectors are rated 15 amps in North America. Do I derate them 
as well or can I draw 15 amps continuous from the C13 connector?



So here is the big question:



If I have a power cord with a NEMA-5-20P at one end, IEC 60320 C13 at the other 
end, and 14awg cordage (rated 18A), can I use/ship this power cord with a 
product rated 15 amps?



Thanks to all.

The Other Brian

________________________________________

LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.



-



-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]><mailto:[email protected]>



All emc-pstc postings are archived and searchable on the web at:

http://www.ieee-pses.org/emc-pstc.html



Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.



Website:  http://www.ieee-pses.org/

Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe) List rules: http://www.ieee-pses.org/listrules.html



For help, send mail to the list administrators:

Scott Douglas <[email protected]><mailto:[email protected]>

Mike Cantwell <[email protected]><mailto:[email protected]>



For policy questions, send mail to:

Jim Bacher:  <[email protected]><mailto:[email protected]>

David Heald: <[email protected]><mailto:[email protected]>



-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]><mailto:[email protected]>



All emc-pstc postings are archived and searchable on the web at:

http://www.ieee-pses.org/emc-pstc.html



Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.



Website:  http://www.ieee-pses.org/

Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe) List rules: http://www.ieee-pses.org/listrules.html



For help, send mail to the list administrators:

Scott Douglas <[email protected]><mailto:[email protected]>

Mike Cantwell <[email protected]><mailto:[email protected]>



For policy questions, send mail to:

Jim Bacher:  <[email protected]><mailto:[email protected]>

David Heald: <[email protected]><mailto:[email protected]>



-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]><mailto:[email protected]>



All emc-pstc postings are archived and searchable on the web at:

http://www.ieee-pses.org/emc-pstc.html



Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.



Website:  http://www.ieee-pses.org/

Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe) List rules: http://www.ieee-pses.org/listrules.html



For help, send mail to the list administrators:

Scott Douglas <[email protected]><mailto:[email protected]>

Mike Cantwell <[email protected]><mailto:[email protected]>



For policy questions, send mail to:

Jim Bacher:  <[email protected]><mailto:[email protected]>

David Heald: <[email protected]><mailto:[email protected]>

________________________________



LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.



-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]><mailto:[email protected]>



All emc-pstc postings are archived and searchable on the web at:

http://www.ieee-pses.org/emc-pstc.html



Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.



Website:  http://www.ieee-pses.org/

Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)

List rules: http://www.ieee-pses.org/listrules.html



For help, send mail to the list administrators:

Scott Douglas <[email protected]><mailto:[email protected]>

Mike Cantwell <[email protected]><mailto:[email protected]>



For policy questions, send mail to:

Jim Bacher:  <[email protected]><mailto:[email protected]>

David Heald: <[email protected]><mailto:[email protected]>

________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to