Maybe these Byzantine definitions are an attempt to reconcile conflicting views on the subject. I agree that they are singularly unhelpful.

John Woodgate OOO-Own Opinions Only
J M Woodgate and Associates www.woodjohn.uk
Rayleigh, Essex UK

On 2017-11-23 01:08, Richard Nute wrote:
For definitions of ELV, SELV, and PELV, I turn to IEC TC64, Electrical 
installations and protection against electric shock, and its publication 61140, 
Protection against electric shock – Common aspects for installation and 
equipment. TC 64 is “to lay down basic safety requirements for protection 
against electric shock for use by technical committees.” IEC 61140 is “… a 
Basic Safety Publication intended for use by technical committees in the 
preparation of standards in accordance with the principles of IEC Guide 104 and 
ISO/IEC Guide 51.”

IEC 61140 defines ELV, SELV, and PELV:

3.26
extra-low-voltage (ELV)
any voltage not exceeding the relevant voltage limit specified in IEC 61201

3.26.1
SELV system
an electrical system in which the voltage cannot exceed ELV:
– under normal conditions; and
– under single-fault conditions, including earth faults in other circuits

3.26.2
PELV system
an electrical system in which the voltage cannot exceed ELV:
– under normal conditions, and
– under single-fault conditions, except earth faults in other circuits

Most product safety standards prohibit access to ELV on the assumption that ELV 
is not adequately separated from a higher voltage.

I admit that I don't understand the statements about earth faults in other 
circuits.  I don't know how an earth fault in another circuit can increase the 
voltage of SELV or PELV.

However, in my reading of 61140, I did not find any requirement that either 
SELV or PELV could or could not be connected to earth.

Rich



-----Original Message-----
From: John Woodgate [mailto:[email protected]]
Sent: Wednesday, November 22, 2017 2:52 PM
To: [email protected]
Subject: Re: [PSES] Safe powering 12V doorlock

The definition of PELV that I have is, I think, from IEC 60364, and it says 
'not electrically separated from earth', which I interpret as meaning 
'connected to earth but not necessarily with a connection that can withstand a 
large fault current'.

You must do as you see fit, but I think that if a potentially fatal fault, 
however improbable, could exist undetected, but could be neutralized by a 
simple earth connection, it would be good practice to provide the earth 
connection.

John Woodgate OOO-Own Opinions Only
J M Woodgate and Associates www.woodjohn.uk Rayleigh, Essex UK




-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to