My understanding isn’t as clear as I would like it to be, so the information I 
am providing is suspect.



I believe that the difference in trip points between North America and Europe 
is due to grounding, wiring and power distribution practices. The power 
distribution systems used in North America allow a trip point of nominally 5 mA 
(4 – 6 mA) without a significant risk of nuisance tripping. However, European 
wiring practices are such that nuisance tripping would be more likely at 5 mA 
and, as such, 30 mA is used as the limit.



Is the 3-phase saw plug connected or field wired? Is it used in a potentially 
wet environment? In North America, portable power distribution units, typically 
used at construction sites, must have protection because it is expected that 
the user will connect power tools that will be used in wet environments. 
However, for a field wired saw installed in a workshop would likely not require 
a GFCI. Much of this comes from the electrical code. Any standards that specify 
the additional protection do so because the code requires it.


Ted Eckert
Microsoft Corporation

The opinions expressed are my own and do not necessarily reflect those of my 
employer.



-----Original Message-----
From: Ralph McDiarmid [mailto:[email protected]]
Sent: Tuesday, January 30, 2018 2:43 PM
To: [email protected]
Subject: Re: [PSES] GFCI vs GFPE



Agreed, and current carry-carrying of PE and bonding of internal parts must 
meet stringent UL/CSA requirements. (not mA!)  It seems to me that 30mA is 
close to lethal, and the GFCI outlets Listed over here are 6mA trip.  (still a 
painful shock)



Ralph McDiarmid

Product Compliance Specialist

Solar Business

Schneider Electric





From: John Woodgate [mailto:[email protected]]

Sent: Tuesday, January 30, 2018 2:30 PM

To: [email protected]<mailto:[email protected]>

Subject: Re: [PSES] GFCI vs GFPE



I don't think that is the reason recognized in Europe. The PE circuit has the 
same (or similar) current-carrying capacity as the line circuit(s), so its 
fault-current capacity for 30 s is very large even for a household supply. I 
think the protector is there to prevent fire and to give some protection 
against electric shock, although the latter is compromised so as to prevent 
nuisance-tripping, which would occur if the trip were set at say 5 mA to give 
much better protection.

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.woodjohn.uk&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853637893&sdata=hM9ZJbor9gxzRIIwUYV0KkogbsHqlWIDv%2BCi2VRAr5I%3D&reserved=0

Rayleigh, Essex UK

On 2018-01-30 22:03, Kunde, Brian wrote:

I’ve recently come to understand that the 30mA Ground-Fault protectors, often 
built into a circuit breaker, is intended to protect the Protective Earth 
(Safety Ground) circuit in the case of a short circuit (opening the circuit 
before the safety ground could be damaged.  It this correct?



Here is my question. I’m evaluating a cut-off saw (5hp) which uses water to 
keep the blade and material cool.  The manufacturer uses a 3-phase 
supplementary circuit breaker which includes the 30mA GFPE option.  This is a 
very expensive part.  When I asked them why they use the GFPE part, they 
couldn’t give me a good answer.



Would such a part be required on a 3-phase motor driven cutoff saw in either 
North America or Europe?  What standard would dictate this?



If the only purpose of a GFPE is to protect the Ground Circuit, on products 
that can handle shorts without damaging the ground circuit, would a GFPE still 
be necessary?



Where are GFPE typically used? What industry?



Please educate me.  This is a new one on me.



Thanks,

Brian



From: Doug Nix [mailto:[email protected]]

Sent: Friday, January 26, 2018 2:48 PM

To: mailto:[email protected]

Subject: [PSES] JOB POSTING - ONTARIO, CANADA



PLEASE CONTACT TED TYCZKA DIRECTLY



A very notable, “high-profile” client who is seeking a Safety & Services 
Sales/Business Development Professional - to join their Machine Services 
Division - the focus of the role is to spearhead/lead the sale of Engineering 
Services related to “functional safety.”



The company sells safety training (workshops), machine assessment/audits, 
engineering design per CSA and/or TUV Safety requirements (“Regulatory 
Compliance”).  The company also sells Remediation and Repair Services (of 
industrial machines) together with Service Contracts ... to customers in the 
aerospace, automotive, forestry, food & beverage, as well as, the packaging 
sectors.



The Safety & Services/Business Development Professional can work from a home 
office - anywhere in Ontario. A Bachelor of Science in Mechanical or Electrical 
Engineering, together with the sale of Machine Safeguard devices and the 
application of these, would be desired ... together, with some exposure to 
Industrial Automation and perhaps Robotics. The key is to have some knowledge 
of safety components, safety scanners, switches, controllers, etc. as well as 
machine building experience.



The employer (a very reputable, Global entity/brand) ... who provide a very 
competitive base salary, lucrative annual bonus/incentive program vs. results, 
plus monthly car allowance, Benefits, Matching RRSP + (Training, Career 
Opportunities and upward mobility).



They are good people, seek an ambitious self-starter who can cover sales from 
the “shop floor” level to the “C Suite” (Boardroom). The company have 
established Sales Reps across Canada ... who can work with the Safety & 
Services Sales Specialist ... this role requires “consultative and solutions 
oriented selling ability.



I will ensure absolute confidentiality. Nice opportunity with a great 
organization and strong, capable leadership. Thanks.



Kind professional regards,

Ted Tyczka



President

Golden Mile Management – Consulting Services

2630 Eglinton Avenue East, Toronto, Ontario M1K 2S3

Tel: (416) 266 - 4434

Email: mailto:[email protected]

Website: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.gmmcs.com%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853637893&sdata=rvAv8X4c%2BEcKm%2BB7ReOa3shnFCrOjHMeT1bV%2FpkTkvg%3D&reserved=0

-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<mailto:[email protected]> All emc-pstc postings are archived and searchable on 
the web at: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853637893&sdata=7XyR1SJPHdKwOwtsKWol8ytxK0DdXiMUUu6hFA%2BuunA%3D&reserved=0

Attachments are not permitted but the IEEE PSES Online Communities site at 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853637893&sdata=S75BzW2dODizRCuBWOFqdanO5xNfPgVmI%2F3yq8uo1oY%3D&reserved=0
 can be used for graphics (in well-used formats), large files, etc.

Website: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853637893&sdata=MECv%2By%2FA5Jw7elBW1NY3RM5wMqqduUkdep3a8emI3ZA%3D&reserved=0

Instructions: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853637893&sdata=XGjmIzKrKRqiwwp5cazKe%2FWifVGLy41Tw%2BOJv5NjJwk%3D&reserved=0

List rules: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853637893&sdata=KmWZISs5OZJqR8qeS7j8hVNqPijatas1sjL7jAex5ZY%3D&reserved=0

For help, send mail to the list administrators:

Scott Douglas <mailto:[email protected]> Mike Cantwell 
<mailto:[email protected]> For policy questions, send mail to:

Jim Bacher <mailto:[email protected]>

David Heald <mailto:[email protected]>

________________________________________

LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<mailto:[email protected]> All emc-pstc postings are archived and searchable on 
the web at: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853637893&sdata=7XyR1SJPHdKwOwtsKWol8ytxK0DdXiMUUu6hFA%2BuunA%3D&reserved=0

Attachments are not permitted but the IEEE PSES Online Communities site at 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853637893&sdata=S75BzW2dODizRCuBWOFqdanO5xNfPgVmI%2F3yq8uo1oY%3D&reserved=0
 can be used for graphics (in well-used formats), large files, etc.

Website: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853637893&sdata=MECv%2By%2FA5Jw7elBW1NY3RM5wMqqduUkdep3a8emI3ZA%3D&reserved=0

Instructions: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=il7Depu73V6753bgNcbXxb%2BUbIx5Hffrm%2FxAu7BWXNM%3D&reserved=0

List rules: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=QjoK%2FhUtAhuDC1WAxtlh%2F2r%2BZNxzTXUyHSxeFISZ%2BHY%3D&reserved=0

For help, send mail to the list administrators:

Scott Douglas <mailto:[email protected]> Mike Cantwell 
<mailto:[email protected]> For policy questions, send mail to:

Jim Bacher <mailto:[email protected]>

David Heald <mailto:[email protected]>





______________________________________________________________________

This email has been scanned by the Symantec Email Security.cloud service.

______________________________________________________________________

-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<mailto:[email protected]> All emc-pstc postings are archived and searchable on 
the web at: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=UESOGWD2YidAklBlE4oJaYAiHUB3B8ZUuqAPMg2i6mI%3D&reserved=0

Attachments are not permitted but the IEEE PSES Online Communities site at 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=wnyIZUbTmBZumRQWew8%2FeSdquIlYyRGSkwgXwNqGs%2F0%3D&reserved=0
 can be used for graphics (in well-used formats), large files, etc.

Website: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=%2FgG543HS49Gci8r4d2g7PbJwe%2FtOPrsgT6%2B2rKzFFDI%3D&reserved=0

Instructions: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=il7Depu73V6753bgNcbXxb%2BUbIx5Hffrm%2FxAu7BWXNM%3D&reserved=0

List rules: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=QjoK%2FhUtAhuDC1WAxtlh%2F2r%2BZNxzTXUyHSxeFISZ%2BHY%3D&reserved=0

For help, send mail to the list administrators:

Scott Douglas <mailto:[email protected]> Mike Cantwell 
<mailto:[email protected]> For policy questions, send mail to:

Jim Bacher <mailto:[email protected]>

David Heald <mailto:[email protected]>



-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>



All emc-pstc postings are archived and searchable on the web at:

https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=UESOGWD2YidAklBlE4oJaYAiHUB3B8ZUuqAPMg2i6mI%3D&reserved=0



Attachments are not permitted but the IEEE PSES Online Communities site at 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=wnyIZUbTmBZumRQWew8%2FeSdquIlYyRGSkwgXwNqGs%2F0%3D&reserved=0
 can be used for graphics (in well-used formats), large files, etc.



Website:  
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=%2FgG543HS49Gci8r4d2g7PbJwe%2FtOPrsgT6%2B2rKzFFDI%3D&reserved=0

Instructions:  
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=il7Depu73V6753bgNcbXxb%2BUbIx5Hffrm%2FxAu7BWXNM%3D&reserved=0
 (including how to unsubscribe)

List rules: 
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C332841906ad44ef66eaa08d5683526de%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529499853647898&sdata=QjoK%2FhUtAhuDC1WAxtlh%2F2r%2BZNxzTXUyHSxeFISZ%2BHY%3D&reserved=0



For help, send mail to the list administrators:

Scott Douglas <[email protected]<mailto:[email protected]>>

Mike Cantwell <[email protected]<mailto:[email protected]>>



For policy questions, send mail to:

Jim Bacher:  <[email protected]<mailto:[email protected]>>

David Heald: <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to