In Europe, the installation codes differ by country. Because the UK uses different wiring techniques (ring-mains) and different wall-sockets (13 A, three rectangular pins) and plugs with in-built fuses, the UK Code, BS 7671, differs more than some of the others do. BS 7671 requires some wall-sockets to include RCDs, and an RCD at the distribution panel. I don't know of any requirement in any British Standard for an RCD inside load equipment.

John Woodgate OOO-Own Opinions Only
J M Woodgate and Associates www.woodjohn.uk
Rayleigh, Essex UK

On 2018-01-31 17:06, Kunde, Brian wrote:

Where Pete stated, “The Euro systems use of RCDs require this protection in many installations (but I’m not familiar with the installation code details)”. This “Code” is probably what I am seeking.

Has anyone run across a Code rule that requires the Product to employ a RCCB within the product?  If the local electrical code requires a RCCB, cannot this protection be provided as part of the site protection?  Why burden the cost of a product where such a requirement may only be necessary in a small percentage of installations?

The main purpose of my question on this topic is cost.  Here in the USA, a GFCI receptacle is very inexpensive; costing around $10 at most home stores.  But a 3-phase RCD Circuit Breaker can cost $300-$400.  On some products, such as a tile saw that uses water, this can more than double the cost of the entire product.  So knowing when and where they are required is very important.

Thanks again to everyone for your consideration.  From what I have read so far on this topic, it is a moving target as electric codes from different states and countries are always evolving and the code governing the requirements of RCDs and GFCIs are common to change.

Thanks,

Brian

*From:*John Woodgate [mailto:[email protected]]
*Sent:* Wednesday, January 31, 2018 11:13 AM
*To:* Kunde, Brian; [email protected]
*Subject:* Re: [PSES] GFCI vs GFPE

You can rely on the recent post in this thread by Pete Perkins.

John Woodgate OOO-Own Opinions Only
J M Woodgate and Associateswww.woodjohn.uk <http://www.woodjohn.uk>
Rayleigh, Essex UK

On 2018-01-31 15:52, Kunde, Brian wrote:

    Thanks for the input everyone.

    I know that GFCI protectors in North America will trip between
    4-6mA. Do other countries, such as Europe, have the same
    requirements?

    Or are 30mA protectors used in Europe? If so, does Europe use 30mA
    ground fault protectors because of nuisance tripping even though
    the studies have shown that 30mA can be fatal?

    These 3-phase cut-off saws that I’m evaluating comes with a power
    cord, but no plug. They can be field wired or a plug could be
    added and plugged it into a receptacle.  The choice is left up to
    the customer.

    The saw uses water but the work environment would not normally be
    considered a “wet location”.  It would not be used in a
    construction location.

    So again, I’m trying to figure out why the saw manufacturer used
    the expensive 30mA ground fault breakers in their product.

    Thanks,

    The Other Brian

------------------------------------------------------------------------


          *LECO Corporation Notice:* This communication may contain
          confidential information intended for the named recipient(s)
          only. If you received this by mistake, please destroy it and
          notify us of the error. Thank you.



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to