There is a motor and a blade, which both move and are linked. In a
cut-off saw, If I have the term right, the whole motor and blade housing
swings on a pivot at the back of the baseplate.
John Woodgate OOO-Own Opinions Only
J M Woodgate and Associates www.woodjohn.uk
Rayleigh, Essex UK
On 2018-01-31 21:33, Nyffenegger, Dave wrote:
I am surprised a basic cut-off saw would fit the definition of
‘machine’ for the MD since cut-off saws (the one’s I’m thinking of)
are basically just a motor with a blade mounted directly to the
armature and I don’t know that the blade is even considered part of
the product. Not really an assembly of linked parts at least one of
which moves, and which are joined together for a specific application.
-Dave
*From:*John Woodgate [mailto:[email protected]]
*Sent:* Wednesday, January 31, 2018 1:58 PM
*To:* [email protected]
*Subject:* Re: [PSES] GFCI vs GFPE
IEC 62841 is a multi-part standard with 23 documents. But it's all
about 'hand-held', so unless the 300 lb product is intended for
Superman or King Kong. they don't apply.
Wiring codes do not specify requirements for load products, except in
very general terms. Safety requirements for products are in product
safety standards.
In Europe, a cut-off saw is a 'machine', so the Machinery Directive
applies. This influences which safety standard is permitted to be
applied to the product.
John Woodgate OOO-Own Opinions Only
J M Woodgate and Associateswww.woodjohn.uk <http://www.woodjohn.uk>
Rayleigh, Essex UK
On 2018-01-31 18:38, Kunde, Brian wrote:
Most interesting. Thanks.
*From:*[email protected] <mailto:[email protected]>
[mailto:[email protected]]
*Sent:* Wednesday, January 31, 2018 1:27 PM
*To:* Kunde, Brian
*Cc:* EMC-PSTC
*Subject:* [BULK] Re: [PSES] GFCI vs GFPE
*Importance:* Low
IEC TC 116 in in the process of folding the 60745-1 (hand held
motor operated tool) standards into the 62841 series (Electric
motor-operated hand-held tools, transportable tools and lawn and
garden machinery). See their dashboard at:
http://www.iec.ch/dyn/www/f?p=103:30:13397277133783::::FSP_ORG_ID,FSP_LANG_ID:4112,25
My reference was not from a part 2, but actually from section
21.16 of 60745-1:
"
Tools employing liquid systems shall protect the user against the
increased risk of
shock due to the presence of liquid under conditions of normal use
and the faults of the liquid
system.
Tools employing liquid systems shall be either:
• of class III construction;
• of class I or class II construction and be provided with a
residual current device and comply
with 14.4, 14.5 and 14.6; or
• of class I or class II construction and be designed for use in
combination with an isolating
transformer and comply with 14.4 and 14.5.
"
Section 14.4 describes using a salt water mix to simulate
overfilling or misassembling and then testing for leakage.
I do not know whether your product falls within scope of 62841;
perhaps your favorite NRTL could help. Your favorite NRTL might
even have someone on the committee who could help with a question.
Mike
------------------------------------------------------------------------
*From: *"Brian Kunde" <[email protected]
<mailto:[email protected]>>
*To: *[email protected] <mailto:[email protected]>
*Cc: *"EMC-PSTC" <[email protected]
<mailto:[email protected]>>
*Sent: *Wednesday, January 31, 2018 11:58:25 AM
*Subject: *RE: [PSES] GFCI vs GFPE
Mike,
Thanks for your offer. I assume the requirement for RCD is limited
to hand-held or portable power tools that uses water. This is
interesting because I didn’t know this was a requirement.
In our case, the cut-off saw we are looking at weighs over 300
lbs. Defiantly not hand-held any probably not considered portable
(depending on your definition).
Do you know if there are similar requirements for non-hand-held
electric saws/tools?
Thanks,
The Other Brian
*From:*[email protected] <mailto:[email protected]>
[mailto:[email protected]]
*Sent:* Wednesday, January 31, 2018 12:29 PM
*To:* Kunde, Brian
*Cc:* EMC-PSTC
*Subject:* Re: [PSES] GFCI vs GFPE
Brian --
I think I've seen a Part 2 standard for 60745-1, as I recall, that
required a RCD if the tool used water and the water ended up in
the wrong place electrically. If you'd like a screen shot of the
section, I can probably find it for you.
Mike Sherman
Graco Inc.
------------------------------------------------------------------------
*From: *"Brian Kunde" <[email protected]
<mailto:[email protected]>>
*To: *"EMC-PSTC" <[email protected]
<mailto:[email protected]>>
*Sent: *Wednesday, January 31, 2018 11:06:36 AM
*Subject: *Re: [PSES] GFCI vs GFPE
Where Pete stated, “The Euro systems use of RCDs require this
protection in many installations (but I’m not familiar with the
installation code details)”. This “Code” is probably what I am
seeking.
Has anyone run across a Code rule that requires the Product to
employ a RCCB within the product? If the local electrical code
requires a RCCB, cannot this protection be provided as part of the
site protection? Why burden the cost of a product where such a
requirement may only be necessary in a small percentage of
installations?
The main purpose of my question on this topic is cost. Here in
the USA, a GFCI receptacle is very inexpensive; costing around $10
at most home stores. But a 3-phase RCD Circuit Breaker can cost
$300-$400. On some products, such as a tile saw that uses water,
this can more than double the cost of the entire product. So
knowing when and where they are required is very important.
Thanks again to everyone for your consideration. From what I have
read so far on this topic, it is a moving target as electric codes
from different states and countries are always evolving and the
code governing the requirements of RCDs and GFCIs are common to
change.
Thanks,
Brian
*From:*John Woodgate [mailto:[email protected]]
*Sent:* Wednesday, January 31, 2018 11:13 AM
*To:* Kunde, Brian; [email protected]
<mailto:[email protected]>
*Subject:* Re: [PSES] GFCI vs GFPE
You can rely on the recent post in this thread by Pete Perkins.
John Woodgate OOO-Own Opinions Only
J M Woodgate and Associateswww.woodjohn.uk <http://www.woodjohn.uk>
Rayleigh, Essex UK
On 2018-01-31 15:52, Kunde, Brian wrote:
Thanks for the input everyone.
I know that GFCI protectors in North America will trip between
4-6mA. Do other countries, such as Europe, have the same
requirements?
Or are 30mA protectors used in Europe? If so, does Europe use
30mA ground fault protectors because of nuisance tripping even
though the studies have shown that 30mA can be fatal?
These 3-phase cut-off saws that I’m evaluating comes with a
power cord, but no plug. They can be field wired or a plug
could be added and plugged it into a receptacle. The choice
is left up to the customer.
The saw uses water but the work environment would not normally
be considered a “wet location”. It would not be used in a
construction location.
So again, I’m trying to figure out why the saw manufacturer
used the expensive 30mA ground fault breakers in their product.
Thanks,
The Other Brian
------------------------------------------------------------------------
*LECO Corporation Notice:*This communication may contain
confidential information intended for the named
recipient(s) only. If you received this by mistake,
please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to <[email protected] <mailto:[email protected]>>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
<http://www.ieee-pses.org/emc-pstc.html>
Attachments are not permitted but the IEEE PSES Online Communities
site at http://product-compliance.oc.ieee.org/
<http://product-compliance.oc.ieee.org/> can be used for graphics
(in well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]>>
Mike Cantwell <[email protected] <mailto:[email protected]>>
For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]>>
David Heald <[email protected] <mailto:[email protected]>>
------------------------------------------------------------------------
*LECO Corporation Notice:*This communication may contain
confidential information intended for the named
recipient(s) only. If you received this by mistake,
please destroy it and notify us of the error. Thank you.
------------------------------------------------------------------------
*LECO Corporation Notice:*This communication may contain
confidential information intended for the named
recipient(s) only. If you received this by mistake,
please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to <[email protected] <mailto:[email protected]>>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
<http://www.ieee-pses.org/emc-pstc.html>
Attachments are not permitted but the IEEE PSES Online Communities
site at http://product-compliance.oc.ieee.org/
<http://product-compliance.oc.ieee.org/> can be used for graphics
(in well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]>>
Mike Cantwell <[email protected] <mailto:[email protected]>>
For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]>>
David Heald <[email protected] <mailto:[email protected]>>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to <[email protected] <mailto:[email protected]>>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
<http://www.ieee-pses.org/emc-pstc.html>
Attachments are not permitted but the IEEE PSES Online Communities
site at http://product-compliance.oc.ieee.org/
<http://product-compliance.oc.ieee.org/> can be used for graphics (in
well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]>>
Mike Cantwell <[email protected] <mailto:[email protected]>>
For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]>>
David Heald <[email protected] <mailto:[email protected]>>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion
list. To post a message to the list, send your e-mail to <[email protected]>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>
For policy questions, send mail to:
Jim Bacher: <[email protected]>
David Heald: <[email protected]>