Uhhh, no, that should be 1500Vdc. Although my power source did go insane for a 
few cycles where the switch had to commutate 2500V peak.

Brian

-----Original Message-----
From: Brian O'Connell [mailto:oconne...@tamuracorp.com] 
Sent: Wednesday, April 04, 2018 10:54 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Need a switch

Did a switch for 1500kVdc that required 6kV dielectric withstand. Used two sets 
of two relays in series, each rated 1500V, actuated through optoisolators. 
Including input and output terminals, was about 20cm x 18cm x7cm. The peak load 
was 280mA, and 10mA continuous. After about 250 power cycles, replaced relays 
for another 200 cycles (completion of test). 'Static' DC switching can be 
stressful to most anything, including MOSFETS.

Brian


From: Ken Javor [mailto:ken.ja...@emccompliance.com]
Sent: Wednesday, April 04, 2018 7:39 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Need a switch

Purpose is to reverse polarity on the charged line in a MIL-STD-461 CS115 
transient generator.  The charged line can charge as high as 2 kV for use, but 
the actual capability is 2.8 kV (2 kVrms output transformer).

Ken Javor
Phone: (256) 650-5261

________________________________________
From: "Grasso, Charles" <charles.gra...@dish.com>
Reply-To: "Grasso, Charles" <charles.gra...@dish.com>
Date: Wed, 4 Apr 2018 14:32:18 +0000
To: <EMC-PSTC@LISTSERV.IEEE.ORG>
Conversation: [PSES] Need a switch
Subject: Re: [PSES] Need a switch

Reminds me of a Frankenstein-like experiment. What exactly is this switch for 
Ken :-D  ??


From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: Wednesday, April 04, 2018 12:50 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Need a switch

This message originated outside of DISH and was sent by: 
owner-emc-p...@listserv.ieee.org

I once had a DPDT knife switch with ceramic base and insulators. Rather big, 
though.

John Woodgate OOO-Own Opinions Only
J M Woodgate and Associates www.woodjohn.uk <http://www.woodjohn.uk>
Rayleigh, Essex UK
On 2018-04-04 04:01, Richard Nute wrote:


Hi Ken:

I interpret your requirement as DPDT, with 3 kV withstand between open contacts 
as well as 3 kV from conductors to accessible parts such as the switch lever.

Tough specs.

Good luck,
Rich

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to