That's right, but at one time, IEC 62368-1 said, effectively, that the
mere presence of a PE contact at the inlet made the product Class I, but
I hope it no longer says, or implies, that.
On 2025-05-20 18:46, Ralph McDiarmid wrote:
Assuming it can be shown through test and inspection using criteria
from the applicable standard(s), it’s Class II.The PE conductor has no
safety function in the example you provide.
*From:*[email protected] <[email protected]>
*Sent:* May 19, 2025 4:06 AM
*To:* [email protected]
*Subject:* [PSES] Safety - Class I or Class II
A product is designed as a Class II product.
But the product has a protective earth (PE) terminal connection. This
PE-connection has no further connection on the PCB. It exists only so
the electricians have a place to connect the PE wire, which always are
present in the AC cable.
Is such a product a Class II or does the PE connection, make it Class I?
BR Amund
------------------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to [email protected]
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/
<https://www.mail-archive.com/[email protected]/%20>
Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how
to unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
List rules:
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]
For policy questions, send mail to:
Jim Bacher at: [email protected]
------------------------------------------------------------------------
To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1>
------------------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to [email protected]
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/
Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how
to unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
List rules:
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]
For policy questions, send mail to:
Jim Bacher at: [email protected]
------------------------------------------------------------------------
To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
--
Best wishes John Woodgate RAYLEIGH Essex OOO-Own Opinions Only
www.woodjohn.uk If something is true: * as far as we know - it's science
*for certain - it's mathematics *unquestionably - it's religion
--
This email has been checked for viruses by AVG antivirus software.
www.avg.com
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
[email protected]
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/
Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
unsubscribe)
List rules:
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]
For policy questions, send mail to:
Jim Bacher: <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1