Hello, colleagues-
I'm looking at hipot testing a physically large electric machine and trying to
determine the best approach to complete the task. NFPA 79 & C22.2 No. 301 say
hipot is required, IEC 60204-1 leaves it to the manufacturer's consideration.
The machine supports outdoor construction work, contains several 3-phase 480V
motors and is powered by on-board genset, all mounted on semi truck trailer.
Process control is done through simple pushbutton switchgear panels. There are
no programmed electronics or PCBs.
This is by far the largest product I've considered for hipot. Isolation of the
product isn't feasible (won't fit on test table :) and disassembly is strictly
limited. I'm looking for practical guidance from those that routinely test and
inspect physically large equipment. IR and ground bond testing are already
planned. Risk assessment thus far tells me hipot may not be essential,
however, the standards say...
How should I address this elephant?
Thanks in advance & best regards,
Chet Summers
________________________________
This electronic message including any attachments ("Message") may contain
information that is privileged, confidential and/or exempt from disclosure
under trade secret and other applicable law. If you are not the intended
recipient, notify the sender immediately, permanently delete all copies of this
Message, and be aware that examination, use, dissemination, duplication or
disclosure of this Message is strictly prohibited. This email and any files
transmitted with it from Charles Machine Works are confidential and intended
solely for the use of the individual or entity to which they are addressed.
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
[email protected]
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/
Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
unsubscribe)
List rules:
https://pses.ieee.org/wp-content/uploads/2024/12/EM-PSTC-List-Rules.pdf
For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]
For policy questions, send mail to:
Jim Bacher: <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1