On 12/31/2015 10:24 PM, John Thornton wrote:
> I went and checked the control transformer and one side is 48v to ground 
> and the other side is 79v to ground. I guess I was confused by that.

I did a quick calculation and if your protective ground has a voltage
with a phase shift of about 62 degrees wrt. the transformer's output and
the open voltage of the transformer is 132V, then one lead will show 48V
(RMS)(*) and the other will show 80V (RMS) with respect to ground.

>From this we can conclude that you are measuring a capacitive coupling.


Calculated from:
Ground potential : V * sin(a + p)
Transformer out A: V * sin(a)
Transformer out B: V * sin(-a)

with:   a = running angle
        p = phase shift
        V = Voltage

Transformer output A wrt. ground:
        V * RMS(sin(a) - sin(a + p))
Transformer output B wrt. ground:
        V * RMS(sin(-a) - sin(a + p))


(*) I assume that your multimeter is measuring root-mean-square (RMS)
voltage in AC mode. That should be a pretty safe assumption.

-- 
Greetings Bertho

(disclaimers are disclaimed)

------------------------------------------------------------------------------
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to