On 01/01/2016 11:37 AM, andy pugh wrote:
> On 1 January 2016 at 17:29, Bertho Stultiens <ber...@vagrearg.org> wrote:
>> The reason for /not/ connecting the ground on a secondary winding is to
>> prevent a capacitively coupled ground path.
> Another reason is that if you connect either secondary winding end  to
> ground using body parts then nothing bad happens. This is the point of
> an isolation transformer.
> If there is an isolation transformer fitted in the machine then
> grounding one of its terminals makes it pointless.
>
Well, it still isolates the 120 V circuit from disturbances 
on the 240 V input.  So, if your building ground to neutral 
has a bunch of noise or offsets between them, the internal 
120 V circuit will be "clean" with respect to the frame ground.

The problem with a totally floating 120 V circuit is that 
various devices plugged in to that system may have somewhat 
large capacitors between hot or neutral and safety ground.  
Very typical in switching power supplies.  Depending on the 
configuration of all the devices on that supply, it could 
cause the neutral to be higher than the hot (with respect to 
ground).  This could cause some equipment to malfunction, if 
they assume the neutral will stay near ground potential.  
Also, a fault in one of the units could persist for some 
time until somebody touches something, and gets a nasty shock.

Open safety grounds are a common problem in the US.  I've 
gotten zapped quite good a few times when touching two 
pieces of equipment at the same time.  Leaving the secondary 
totally floating is kind of the same thing.  In the UK, they 
ground the center tap of those job site transformers for 
exactly this reason.

Now, when testing inside power equipment using an isolation 
transformer so you can use a scope on a switching power 
supply, for instance, then you DO want the transformer 
secondary floating.

Jon

------------------------------------------------------------------------------