On 02/08/2017 11:34 AM, [email protected] wrote:
> I don't have a physical stop on my Z axis, putting one in would be a PITA.  
> The drive is exceptionally strong and it would be problematic to stop the 
> axis that way.  If you're an idiot and jog it that way prior to homing, you 
> can dismount the axis.
>
> There is a homing switch at Z+.  It sounds desirable to halt + movement when 
> that switch is tripped, AND not homed, AND not in the actual homing sequence. 
>  But NOT stop - movement, otherwise you'd jog it upwards, get it stuck, and 
> no way to jog down.
>
> How difficult would it be to do that?
>
>
LinuxCNC includes provisions for this.  Set 
HOME_IGNORE_LIMITS = YES in the .ini file for that axis.
The trick, of course, is to make sure the home position is 
moved off that switch.  So, you have to set a
HOME_OFFSET = -0.1

or something like that, so it jogs off the home switch 
sufficiently to UN-trip the switch.
Then, set your MAX_LIMIT to less than that distance (or zero).

This way, it will home up to the switch, move down by the 
HOME_OFFSET amount and then set soft limits so you cannot 
reach the switch.