On Tue, 16 May 2017, Bertho Stultiens wrote:

> Date: Tue, 16 May 2017 21:03:00 +0200
> From: Bertho Stultiens <ber...@vagrearg.org>
> Reply-To: "Enhanced Machine Controller (EMC)"
>     <emc-users@lists.sourceforge.net>
> To: "Enhanced Machine Controller (EMC)" <emc-users@lists.sourceforge.net>
> Subject: Re: [Emc-users] switching to a slower spi driver to see if it works,
> 
> On 05/16/2017 08:33 PM, Peter C. Wallace wrote:
>> 50 MHz will work if everything is terminated correctly and if the RSPI timing
>> is correct. (It may require using a SPI late data sample option if the RSPI
>> hardware has that option)
>>
>> Correct series termination of RSPI outputs (130 Ohm total for 0.050" flat
>> cable) depends on the output impedance of the RSPI outputs so there's no
>> guarantee that the added 87 ohms is correct (this may also depend on RSPI
>> output drive strength settings if such things exist on the RSPI)
>
> Well, in theory, that is true. I suspect that there is a phase-reversal
> problem at these high frequencies. The probe of the scope adds just
> enough capacity to delay the signal by a fraction.
>
> At 50MHz clock, you have a phase margin of <10ns. This time is consumed by:
> - the wire-connection (~2ns per meter for copper),
> - the round-trip in the slave tranceiver (the 7i90 SPI interface),
> - the RPI buffers and SPI tranceiver.
>
> Lets assume that the wire, including PCB traces etc., takes 1ns
> (roundtrip for 25 cm). The RPI buffers and shift register are probably
> around 2ns and a bit more if it contains a glitch-filter. The 7i90
> interface has both input buffer, an output buffer and at least one
> flip-flip propagation delay. My guess is that it would be about 0.5ns +
> 0.5ns + 2ns.
>
> That brings the grand total to 6ns, which is at 60% of the phase margin.
> This is an optimistic estimation where I specifically disregarded setup-
> and hold-times, which make things much worse. Assuming setup- and
> hold-margins on both ends (round-trip) of 0.5ns means adding another
> 2ns, resulting in 8ns total time and 80% of the phase margin. This is
> getting close to the failure point.
>
> Adding just a bit of capacity at the wrong place will make the signal
> (seemingly) slower because the flanks are less steep (as seen on the
> scope). This is enough to cause the system to fail.
>
> This also means that you cannot add external line-buffers on the lines.
> These would simply add to much delay at these frequencies (something
> like 6...10ns). Unfortunately, SPI is a synchronous and timing-bound
> propocol and cannot tolerate phase reversal.
>
>
> -- 
> Greetings Bertho
>
> (disclaimers are disclaimed)
>
> ------------------------------------------------------------------------------
> Check out the vibrant tech community on one of the world's most
> engaging tech sites, Slashdot.org! http://sdm.link/slashdot
> _______________________________________________
> Emc-users mailing list
> Emc-users@lists.sourceforge.net
> https://lists.sourceforge.net/lists/listinfo/emc-users
>


All fine except that Gene said that slowing the clock (with added capacitance) 
made the interface work. If this were a clock --> read data timing issue, 
slowing the clock edges with added capacitance would make things worse.

So I think its more likely a signal integrity issue, though as you say 50 MHz 
is probably pushing it. I've run the 7I90 slave SPI interface for weeks at 50 
MHz with a FPGA master, but the FPGA master has the "late sample read data" 
option, not sure the RSPI has this or if its used




Peter Wallace
Mesa Electronics


------------------------------------------------------------------------------
Check out the vibrant tech community on one of the world's most
engaging tech sites, Slashdot.org! http://sdm.link/slashdot
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users