On 9/23/22 17:24, gene heskett wrote:
Each brand of vfd seems to have its own setup. But that lf boost is a tricky one. I don't know if that invertor shows you the amperage being delivered but it seems it would be an odd one if it didn't. What you normally do is read the motors nameplate for the FLA, Full Load Amperage.

Then set the lf boost to not exceed that.
Yes, I have found that the default current limit is 3 A, my 2 HP motor is rated at 6 A, so that was the reason for the trips.

If you intend to use it in both directions, quickly as in rigid tapping operations, the accel/decel registers are generally set rediculously conservative. Those can be sped up to almost instant,
but lcnc can still confuse the vfd into tripping.

I have a lowpass filter on the spindle speed value in the HAL file.  This has worked great on my old mill.  I did have to turn off the motor overheat integrator in the old VFD, as the Bridgeport motors can handle plug reversing.  I do 4-40 rigid tapping at 1000 RPM.  I will have to figure out how to do that on the new VFD.

Thanks,

Jon