> Because 6 AWG with 90 deg C insulation allows supply up to 75A which is
> probably what those public EVSE are designed to support even though they
> are connected to 50A breaker and are configured to supply not more than 30
> or 40A (the duty cycle setting of the pilot signal).
>
> Having a 10 AWG cord allows 40A if the insulation is 90 deg C, otherwise
it is
> 30A max, see for example the table at
> http://en.wikipedia.org/wiki/American_wire_gauge

That table is for one solid wire, not stranded or multiwire conductors. The
NEC Table 400.5 (A) and (B) also derate by 20% IIRC, when there are 2
current carrying conductors in the same cable.

The J1772 SAE Specs the EVSE cord - "The wiring insulation shall be rated
for 105 °C", not 90C. I've got some 105 deg C tables (not NEC) that state
that 10 AWG, 2 current carrying conductors, is actually rated at 46.6A.

Rush
www.TucsonEV.com