> Are you discussing the wiring to the EVSE or the cable to the car?
> The NEC requires long wire runs to be derated to minimize voltage drop.  I
> suspect that is the reason for #6 wire.

Concerning the cable length from the EVSE to the car the SAE J1772 Standard
states that "The cordset length shall be in accordance with NEC 625".  NEC
625.17 Cable states "The overall length of the cable shall not exceed 7.S m
(25 ft) unless equipped with a cable management system that is listed as
suitable for the purpose."

Rush