At 07:04 -0700 5/27/09, w_tom wrote:
>  A UPS in battery backup mode can output some of the 'dirtiest'
>electricity a computer may see.  For example, this 120 volt UPS
>outputs two 200 volt square waves with a spike of up to 270 volts
>between those square waves; called a modified sine wave.  No problem
>for any computer.  But may be destructive to surge power strips.

Analysis:

w_tom must be using the 200V figure to represent the peak to peak voltage of 
the square wave. That's the difference between minus 100 volts and plus 100 
volts with respect to the common wire and is what one would measure with an 
oscilloscope.

The 120 volt value is called an RMS, for root mean square, voltage of what it 
quite close to a sine wave that is provider by the power company. The peak to 
peak voltage of that wave is 2 * sqrt(2) * 120 or 339 volts. RMS is used 
because it gives the same answers for heating power of a DC voltage with the 
same value as the RMS AC. A 120 volt incandescent lamp doesn't care if it gets 
120 V RMS or 120 volts DC. Calculus-enabled folks will recognize RMS as as the 
square root of the integral of the square of the wave over one cycle.

The "modified sine wave" is pretty bad but those circuits do pretty well at 
making the RMS value of their "square" waves come out to 120 V. What they do is 
modify the time ratio between on and off in response to the demand of the load. 
The waveform should be described as rectangular rather than square.

Computers are happy with rectangular waves. In fact they would be happy with DC 
at about 339 volts. Motors are an entirely different story because the harmonic 
content of modified sine waves just heats them up without creating mechanical 
energy. That's one reason for 12 volt DC fans these days.

The spikes from a UPS are not supposed to be there. They typically come from 
sudden interruption of current in an inductive load. That's not a computer but 
might be a motor or a badly designed transformer in the UPS.  270 volts is not 
terribly high but if repeated regularly it might damage the metal-oxide 
varistors that are placed in surge protectors after the UPS.

-- 

--> In Christianity, man can have only one wife. This is known as monotony. <--

--~--~---------~--~----~------------~-------~--~----~
You received this message because you are subscribed Low End Mac's G3-5 List, a 
group for those using G3, G4, and G5 desktop Macs - with a particular focus on 
Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to [email protected]
To unsubscribe from this group, send email to 
[email protected]
For more options, visit this group at 
http://groups.google.com/group/g3-5-list?hl=en
Low End Mac RSS feed at feed://lowendmac.com/feed.xml
-~----------~----~----~----~------~----~------~--~---

Reply via email to