On May 29, 12:56 pm, Doug McNutt <[email protected]> wrote:
> Analysis:
> ...
> The real problem with MOVs is that they will only handle a few hundred such 
> pulses
> in their lifetime. Some manufacturers add a green LED to their boxes as an
> indicator that the MOV has been damaged too many times.

 Numerous pulses applied to an MOV only degrade it.  A degraded MOV is
not reported by that LED.  That LED indicates the MOV was subjected to
a surge massively in excess of what the manufacturer defines
acceptable.  A failed MOV also has its voltage changed by 10% (as
stated in manufacturer datasheets).  MOV is still functional and that
light does not report the degradation.  That light can only report a
completely unacceptable failure - a one time massive current in excess
of the manufacturer's Absolute Maximum Parameters.  LED can only
report one type of failure because the MOV was grossly undersized.

  Using same datasheets, a 270 volt spike on a 200 joule MOV for 1
millisecond will degrade that MOV in two pulses.   Obviously that 270
volts spike will be less when conducted through that MOV.   270 volts
for 1 millisecond through a light bulb is not a valid analysis.  Your
analysis must put that voltage across the MOV.  Since current limit
for that 270 volt spike is not known, then insufficient information
exists to perform an analysis.   This worst case analysis for a 200
joules MOV can only withstand two 270 volts spikes - from manufacturer
datasheets.

   Surges are current - not voltage events.  Voltage will rise as
necessary to conduct that current.  Two kilovolt isolation in a
network card or power supply is not exceeded if that current has some
other path to earth.  Just like the church steeple.  Lightning voltage
(and therefore energy dissipation) is minimal on a church steeple if
conducted to earth by Franklin's invention.  'Whole house' protector
also does diverting to earth for a computer's power supply.  UPS does
not.

  ATX power supply (like all appliances) has internal protection.  But
that protection can be overwhelmed (voltage will increase) IF surge
current is not diverted to earth.

  A dike cannot stop a flood.  But a dike works if the flood has a
downriver path.  Same principle applies to a computer's power supply
when downriver is a properly earthed 'whole house' protector.

  Bottom line: a protector is only as effective as its earth ground.
Which is why all facilities that cannot suffer damage connect
protectors short to an even better earthing electrode.

--~--~---------~--~----~------------~-------~--~----~
You received this message because you are subscribed Low End Mac's G3-5 List, a 
group for those using G3, G4, and G5 desktop Macs - with a particular focus on 
Power Macs.
The list FAQ is at http://lowendmac.com/lists/g-list.shtml and our netiquette 
guide is at http://www.lowendmac.com/lists/netiquette.shtml
To post to this group, send email to [email protected]
To unsubscribe from this group, send email to 
[email protected]
For more options, visit this group at 
http://groups.google.com/group/g3-5-list?hl=en
Low End Mac RSS feed at feed://lowendmac.com/feed.xml
-~----------~----~----~----~------~----~------~--~---

Reply via email to