>>>>> "Clinton" == Clinton N Fell <[EMAIL PROTECTED]> writes:
Clinton> So the above should show 2.4KW for a wall outlet and 12KW for a Clinton> breaker box. Actually, most NEMA outlets are connected via a 15A breaker or fuse, not 20A. If it is 20A, the socket will look like « ├ │ »; 15A look like « │ │ ». (A 20A plug looks like: « ─ │ ».) (That utf-8 art really ought to have a ground pin as well, of course. In each case below center.) The main breakers/fuses are 100A for each of the two spans; but one is only expected to draw 80A -- the rest is to cover short surges. Finally, it is officially 115V service -- meaning they only have to post paperwork to the gov't when the voltage drops below 115V -- and most places I've measured w/in a city or village have had 125 to 127 volts at the sockets. The highest I've personally measured was 132V. So, you should be able to draw at least 1.725 kVA, but often up to 1.9 kVA from a single residential circuit. From the main lines into the residence you should be able to draw at least 23 kVA, up to 25.4 kVA. And a max of 26.4 kVA if the site is *very* close to a substation. I think it is safe to assume that Draw Power has a power factor of 1.0, so you can safely read kW for kVA. As per «http://sjgames.com/errata/gurps/grimoire.html», that makes for 3 to 3.5 minutes per FT from a socket, and 14 to 16 seconds per FT for the mains. Say 3 minutes per FT and 4 FT per minute for game purposes. The above covers G3 TL7, early TL8, and probably at least the last half of TL6. For G4 call that 7, 8 and the last third or so of 6. Whether more power will be provided at higher TLs is world-dependant. Specifically on how much power the typical residence is likely to use. BTW, Essential Solar Cells should be good for 10 FT per hour per m², if on Terra and at the equator. ☺ -JimC -- James Cloos <[EMAIL PROTECTED]> _______________________________________________ GurpsNet-L mailing list <[email protected]> http://mail.sjgames.com/mailman/listinfo/gurpsnet-l