On Mar 22, 2007, at 4:32 PM, Prof. Jose Roberto Camacho wrote:

I didn't have the case9 here, but running a power-flow (a non- linear set of equations) you can leave your power generation at zero (active and reactive) in the slack bus (reference bus), in matpower you can have more than one. As an iterative process, on a slack bus (reference bus) you specify voltage (1 pu) and angle (zero), generator active and reactive powers in the slack bus will be function of the voltages obtained in other bars and the losses. In agreement with all the equations of your non-linear system describing the system.

Run your case9 model, and look if the powers remains the same after convergence (at the
end of the routine).

Just one small additional clarification. There are two separate concepts here that are often combined, and in fact they are combined in the MATPOWER implementation of the power flow.

(1) Voltage angle reference bus -- Since the power flow equations essentially only deal with angle differences, a single arbitrary reference is necessary in each "island" in the network to uniquely solve for the remaining voltage angles. Normally, you would only want to specify more than one angle reference if you have multiple unconnected islands.

(2) Real power slack -- When computing the power flow for an N-bus system, where Q is specified at all load buses and V is specified at the remaining buses and a reference angle is specified at the reference bus, specifying P at every bus would leave us with 2N equations [a] and 2N-1 unknowns [b]. A simple approach to solve this is to allow P at a single bus to be a variable that takes up the "slack". Conceptually, this could be any generator bus. I does not have to be the same bus used for (1). It is also possible to allow P to be free at multiple buses if we include additional equations defining how the slack is to be distributed. Again this is independent of (1).

One more point, an optimal power flow formulation needs (1) but not (2), and in MATPOWER's implementation the reference bus is exactly that. The power flow problem, on the other hand needs both (1) and (2), and in the MATPOWER implementation the reference bus serves as both.


[a] P and Q balance at each bus
[b] V at load buses, Q at remaining buses and angle at all buses except the reference


--
Ray Zimmerman
Senior Research Associate
428-B Phillips Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645



Reply via email to