Hi there,

I have some generator data- LV MVAr Limit: Lag = 409, Lead = -187.  Is this the
data which would go in columns 4 and 5 generator input?

thanks,

shane.








Quoting Ray Zimmerman <[email protected]>:

> That is the correct field to enter the generation info. But, if bus 1  
> is set as the slack bus, the entered value for gen 1 will be ignored  
> and replaced by the computed value (equal to load minus losses minus  
> sum of other generation). If you want to specify the generation at  
> bus 1 and allow one of the other generators to be the slack, just  
> change the type of bus 1 to 2 and change one of the other generator  
> buses to type 3.
> 
> Hope this helps,
> 
>       Ray
> 
> On Mar 23, 2007, at 11:37 AM, [email protected] wrote:
> 
> >
> > Ray,
> >
> > Yes that makes sense to me, but i'm till struggling with the idea  
> > of this
> > 'slack' for the real power, because if the generator info is not  
> > entered in that
> > field then how does MATPOWER know the generator output?
> >
> > thanks.
> >
> > shane.
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> > Quoting Ray Zimmerman <[email protected]>:
> >
> >> On Mar 22, 2007, at 4:32 PM, Prof. Jose Roberto Camacho wrote:
> >>
> >>> I didn't have the case9 here, but running a power-flow (a non-
> >>> linear set of equations) you can
> >>> leave your power generation at zero (active and reactive) in the
> >>> slack bus (reference bus), in
> >>> matpower you can have more than one. As an iterative process, on a
> >>> slack bus (reference
> >>> bus) you specify voltage (1 pu) and angle (zero), generator active
> >>> and reactive powers in the
> >>> slack bus will be function of the voltages obtained in other bars
> >>> and the losses. In agreement
> >>> with all the equations of your non-linear system describing the
> >>> system.
> >>>
> >>> Run your case9 model, and look if the powers remains the same after
> >>> convergence (at the
> >>> end of the routine).
> >>
> >> Just one small additional clarification. There are two separate
> >> concepts here that are often combined, and in fact they are combined
> >> in the MATPOWER implementation of the power flow.
> >>
> >> (1) Voltage angle reference bus -- Since the power flow equations
> >> essentially only deal with angle differences, a single arbitrary
> >> reference is necessary in each "island" in the network to uniquely
> >> solve for the remaining voltage angles. Normally, you would only want
> >> to specify more than one angle reference if you have multiple
> >> unconnected islands.
> >>
> >> (2) Real power slack -- When computing the power flow for an N-bus
> >> system, where Q is specified at all load buses and V is specified at
> >> the remaining buses and a reference angle is specified at the
> >> reference bus, specifying P at every bus would leave us with 2N
> >> equations [a] and 2N-1 unknowns [b]. A simple approach to solve this
> >> is to allow P at a single bus to be a variable that takes up the
> >> "slack". Conceptually, this could be any generator bus. I does not
> >> have to be the same bus used for (1). It is also possible to allow P
> >> to be free at multiple buses if we include additional equations
> >> defining how the slack is to be distributed. Again this is
> >> independent of (1).
> >>
> >> One more point, an optimal power flow formulation needs (1) but not
> >> (2), and in MATPOWER's implementation the reference bus is exactly
> >> that. The power flow problem, on the other hand needs both (1) and
> >> (2), and in the MATPOWER implementation the reference bus serves as
> >> both.
> >>
> >>
> >> [a] P and Q balance at each bus
> >> [b] V at load buses, Q at remaining buses and angle at all buses
> >> except the reference
> >>
> >>
> >> -- 
> >> Ray Zimmerman
> >> Senior Research Associate
> >> 428-B Phillips Hall, Cornell University, Ithaca, NY 14853
> >> phone: (607) 255-9645
> >>
> >>
> >>
> >>
> >>
> >
> >
> >
> >
> >
> 
> 
> 




Reply via email to