The voltage is given 4.16kV. I convert the impedances to p.u. by myself with
1MVA base. Actually I have checked this model in 'runpf()' and the result is
almost the same as shown in IEEE 123 node profile. So I guess the problem
might be the generation cost setting. I'm trying to fix that problem.

Thank you very much!


*Fanjun Meng
Electrical Engineering
Missouri University of Science & Technology
[email protected] <[email protected]>*



On Wed, Jun 29, 2011 at 2:39 AM, Simon Schneider <[email protected]>wrote:

> **
> Are the nodal voltage limits set wide enough(e.g. 0.9 an 1.1)?
> Another possible source could be a bad choice of baseMVA and base voltage.
> Do you convert the impedances  by yourself or are they already given in
> p.u?
>
> Regards,
> Simon
> Am 6/28/2011 10:05 PM, schrieb Fanjun Meng:
>
> Thanks a lot!
>
> *Fanjun Meng*
>
>
>
> On Tue, Jun 28, 2011 at 12:36 PM, Santiago Torres <[email protected]
> > wrote:
>
>> Maybe the generation costs you are using for the opf are causing
>> problems.  Try to check that!.
>>
>> Regards,
>>
>>  Santiago
>>
>>   2011/6/28 Fanjun Meng <[email protected]>
>>
>>> Thank you very much for your suggestion!
>>> Actually I did check the simple power flow result with constraints, the
>>> voltages, line flows, generations are all satisfied. That's why I'm confused
>>> with this problem. Is it possible that the line impedences and system
>>> topology may cause matrix sigularity during OPF calculation iteration and
>>> fail to converge?
>>>
>>> Thanks a lot!
>>>
>>> *Fanjun Meng
>>> *
>>>
>>>
>>>
>>>
>>> On Tue, Jun 28, 2011 at 10:13 AM, Santiago Torres <
>>> [email protected]> wrote:
>>>
>>>> The simple power flow has not constraints, so maybe with the settings
>>>> you are using the power flow converges and has solution, however when
>>>> you use the opf, some constraints can cause it does not converge.  Check if
>>>> the IEEE 123 node reported solution when using the simple power flow
>>>> is complying the constraints (ie voltages, power generation, power flows).
>>>>
>>>> I hope this can help.
>>>>
>>>> Santiago Torres
>>>>
>>>>   2011/6/28 Fanjun Meng <[email protected]>
>>>>
>>>>> Hello,
>>>>>
>>>>> I've been working on IEEE 123 nodes system and created a model for
>>>>> MatPower power flow. This model is basically a radial distribution system
>>>>> with a single generation at substation and works fine when I can use
>>>>> runpf(), and it returns similar result as shown IEEE 123 node system 
>>>>> report.
>>>>> However, when I use the same model for runopf(), it shows
>>>>>
>>>>>
>>>>> Numerically Failed
>>>>> Did not converge in 4 iterations.
>>>>> Did not converge (0.10 seconds)
>>>>>
>>>>> The total generation is very different from total demand, and bus
>>>>> voltages are at strange values (e.g. 1.836p.u. at reference bus). Also,
>>>>> generation cost Lambda are extremely high (e.g. 17528752586.76 $/MWh @ bus
>>>>> 6). I have tried to add multiple DGs at different locations and change the
>>>>> system to a ring type system, but it didn't work out. Does anyone have any
>>>>> suggestions or experiences to this problem? Your help is highly 
>>>>> appreciated!
>>>>>
>>>>> Have a good day!*
>>>>>
>>>>> Fanjun Meng
>>>>> *
>>>>>
>>>>>
>>>>
>>>>
>>>>  --
>>>> Dr.-Ing. Santiago Torres
>>>> IEEE Senior Member
>>>>
>>>> Post-Doctoral Fellow
>>>> School of Electrical and Computer Engineering
>>>> University of Campinas, Campinas, SP, Brazil
>>>>
>>>> http://www.dsee.fee.unicamp.br/
>>>>
>>>> Albert Einstein, 400
>>>> 13083-852, Campinas, SP, Brazil
>>>>
>>>
>>>
>>
>>
>> --
>> Dr.-Ing. Santiago Torres
>> IEEE Senior Member
>>
>> Post-Doctoral Fellow
>> School of Electrical and Computer Engineering
>> University of Campinas, Campinas, SP, Brazil
>>
>> http://www.dsee.fee.unicamp.br/
>>
>> Albert Einstein, 400
>> 13083-852, Campinas, SP, Brazil
>>
>
>
>

Reply via email to