On Wed, Jun 6, 2012 at 5:20 PM, Idris Musa <[email protected]>wrote:

> Hi iman,
> The values  R and X in mpc.branch matrix are  per unit quantities. If you
> have R and X given in ohms/km the effective values in ohms must be
> converted to per unit impedance. The base impedance can be calculated from
> the given or assumed  Base MVA and Base voltage. Given the sequence
> impedance, it is enough to use the positive sequence R and X and convert to
> per unit impedance assuming the  network is transposed. Which the
> assumption used in MATPOWER power flow  computation.
> Hope this will help.
> Idris
> ________________________________________
> From: [email protected] [
> [email protected]] On Behalf Of iman [
> [email protected]]
> Sent: 06 June 2012 15:06
> To: MATPOWER discussion forum
> Subject: Branch positive and negative sequence resistance and reactance
>
> Dear All,
>
> 1-In mpc.branch do r and x represent positive and negative sequences or
> zero sequences?
> 2- Are r and x per Kilometer or not?
>
> Thanks
> Iman
>
>
>


-- 
Best regards
Iman

Reply via email to