Thank you. If the lines' limitations is dependent to system, before running 
OPF, how can we determine which one (thermal or stability) is more restricting 
to set in RATE_A?

-Reza 


________________________________
 From: Ray Zimmerman <[email protected]>
To: MATPOWER discussion forum <[email protected]> 
Sent: Friday, October 5, 2012 6:19 AM
Subject: Re: comprehension question about RATE_A, RATE_B, RATE_C
 

I believe it depends on the system and on the individual line. Presumably, you 
would set RATE_A to the less of the two limits.

-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Oct 5, 2012, at 8:48 AM, Mohammad Reza Salehizadeh 
<[email protected]> wrote:

As we know, there are two restricting constraints for the MVA flows a 
transmission line: a) Thermal limitation b) Stability limitation that (b) is 
more restricted. As Ray stated, currently MATPOWER consider RATE_A. Hence, Is 
it more reasonable to consider Stability limitation in RATE_A for short or 
mid-term power system analysis?
>
>
>-Reza
>
>
>
>________________________________
> From: Ray Zimmerman <[email protected]>
>To: MATPOWER discussion forum <[email protected]> 
>Sent: Friday, October 5, 2012 5:39 AM
>Subject: Re: comprehension question about RATE_A, RATE_B, RATE_C
> 
>
>The only one that is used currently by MATPOWER is the long term rating 
>(RATE_A), which is used to limit the MVA flows when running an OPF.
>
>
>-- 
>Ray Zimmerman
>Senior Research Associate
>419A Warren Hall, Cornell University, Ithaca, NY 14853
>phone: (607) 255-9645
>
>
>
>
>On Oct 4, 2012, at 9:51 AM, Cansu Yildirim <[email protected]> wrote:
>
>Dear All,
>> 
>>I’m trying to model a network containing different voltage levels and I have 
>>to take account of the load of each branch in my network, so that my lines 
>>are not overloaded.
>>Therefore I wanted to fill in data for the long, short and emergency ratings 
>>(RATE_A,RATE_B,RATE_C). As far as I didn’t get anything wrong, these ratings 
>>define the allowable magnitude of the flow. Can anybody give me a proper 
>>definition? And how do they influence my power flow? How does matpower use 
>>this information?
>>And I’m not sure how to calculate these ratings. Is it enough to know the 
>>maximum allowable operating current and voltage rating for the cables?
>> 
>>I would be grateful for any help.
>> 
>>Kind regards,
>> 
>>Cansu Yildirim
>
>
>