Dear Dr. Ray,

 

Speaking of the modeling transformer and phase shifter, I would like to see
if the adjustment of the two parameters (tap ratios and shift angles) along
with the generators and loads could get better results of OPF in terms of
cost and convergence (due to the line limits in some cases). do you have any
suggestions as to how to make the tap ratios and shift angles as variables
in the OPF without using iterative calculation (like blindly or using some
heuristic algorithms to modify them and redo the OPF)? If I understand it
correctly, these two values are fixed before the PF & OPF calculation in
terms of Y matrix at present in Matpower. 

 

I was considering to model the transformer/ phase shifter as two generators
in respect to the flow limits, but it may split the network into two islands
in some cases. So, do you have any suggestion on this as well? I guess it
also applies to the DC line when it is the only connection between two parts
of the network.

 

Thanks a lot 

 

Best wishes,

 

Tao

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Ray Zimmerman
Sent: Tuesday, April 16, 2013 2:31 PM
To: MATPOWER discussion forum
Subject: Re: Modelling transformer and phase shifter

 

Yes, for a transformer you will typically have an off-nominal taps ratio,
i.e. branch(b, TAP) ~= 1 (or 0, which signifies a normal transmission line).
Similarly, if you have a phase shift, you will have branch(b, SHIFT) ~= 0.

 

How the transformer TAP and SHIFT parameters affect the amount of load able
to be dispatched depends on the network, so it could go either way.

 

-- 

Ray Zimmerman

Senior Research Associate

419A Warren Hall, Cornell University, Ithaca, NY 14853

phone: (607) 255-9645









 

On Apr 16, 2013, at 8:18 AM, Jiashen Teh <[email protected]>
wrote:





Dear Dr Ray,

According to your manual , in section '3.2 Branches'

it is mentioned that:

 

'All transmission lines, transformers and phase shifters are modeled with a
common branch model......'

Does this mean, if I want to include modelling of transformer at a branch, I
would set the column 9 and 10 of mpc.branch which govern the transformer
turn ratio, N ?

I notice that for values other than zero for both columns (in a manner to
increase N or reduce N), the network (6 bus) will encounter increase of load
not able to be dispatched. Isn't is load dispatch-able should increase?

                
Yours sincerely,

Jiashen Teh

 