It is correct that in the current MATPOWER OPF, the TAP and SHIFT parameters 
are fixed input parameters, not variables. I don't think there is a way to fake 
it with the AC OPF. That is, I think you really need to include them as 
variables in the flow equations and corresponding derivatives. There may be a 
way to fake it with dummy injections in the DC OPF, but I haven't really 
thought about it carefully.

Please let us know if you come up with something that works. And of course, 
others can feel free to suggest ideas.

-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Apr 16, 2013, at 9:04 AM, Tao HUANG <[email protected]> wrote:

> Dear Dr. Ray,
>  
> Speaking of the modeling transformer and phase shifter, I would like to see 
> if the adjustment of the two parameters (tap ratios and shift angles) along 
> with the generators and loads could get better results of OPF in terms of 
> cost and convergence (due to the line limits in some cases). do you have any 
> suggestions as to how to make the tap ratios and shift angles as variables in 
> the OPF without using iterative calculation (like blindly or using some 
> heuristic algorithms to modify them and redo the OPF)? If I understand it 
> correctly, these two values are fixed before the PF & OPF calculation in 
> terms of Y matrix at present in Matpower.
>  
> I was considering to model the transformer/ phase shifter as two generators 
> in respect to the flow limits, but it may split the network into two islands 
> in some cases. So, do you have any suggestion on this as well? I guess it 
> also applies to the DC line when it is the only connection between two parts 
> of the network.
>  
> Thanks a lot
>  
> Best wishes,
>  
> Tao
>  
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ray Zimmerman
> Sent: Tuesday, April 16, 2013 2:31 PM
> To: MATPOWER discussion forum
> Subject: Re: Modelling transformer and phase shifter
>  
> Yes, for a transformer you will typically have an off-nominal taps ratio, 
> i.e. branch(b, TAP) ~= 1 (or 0, which signifies a normal transmission line). 
> Similarly, if you have a phase shift, you will have branch(b, SHIFT) ~= 0.
>  
> How the transformer TAP and SHIFT parameters affect the amount of load able 
> to be dispatched depends on the network, so it could go either way.
>  
> -- 
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> 
>  
> On Apr 16, 2013, at 8:18 AM, Jiashen Teh <[email protected]> 
> wrote:
> 
> 
> Dear Dr Ray,
> 
> According to your manual , in section '3.2 Branches'
> it is mentioned that:
>  
> 'All transmission lines, transformers and phase shifters are modeled with a 
> common branch model......'
> 
> Does this mean, if I want to include modelling of transformer at a branch, I 
> would set the column 9 and 10 of mpc.branch which govern the transformer turn 
> ratio, N ?
> 
> I notice that for values other than zero for both columns (in a manner to 
> increase N or reduce N), the network (6 bus) will encounter increase of load 
> not able to be dispatched. Isn't is load dispatch-able should increase?
>                 
> Yours sincerely,
> 
> Jiashen Teh
> 
>  

Reply via email to